Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
If it's a service rated ATS, then it doesn't matter, the breaker in the ATS will protect it. If it's not service rated, then an OCPD ahead of it is required that is properly rated. In this case, 200 amps. If you are using fuses as the OCPD, then I think that a sign on the disconnect such as "maximum safe fuse size is 200 amps" would be sufficient.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
There is also a physical size difference between 400 and 200 amp fuses.
 