single pole load/circuit two pole switch

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Yes, it can disconnect both conductors or just the ungrounded conductor.

Roger
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I have mechanical equipment 277V single phase and disconnect for the mechanical equipment is two pole. Would this be correct?
277 1ph is the line-to-neutral voltage of 480v line-to-line. Thus, with a line-to-neutral circuit, only a 1p disconnect is required.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
277 1ph is the line-to-neutral voltage of 480v line-to-line. Thus, with a line-to-neutral circuit, only a 1p disconnect is required.
I have 2 pole disconnect 277V 1 ph.

Anywhere in code says 1p disconnect required for 277V 1 ph?

Sent from my SM-G935U using Tapatalk
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You can disconnect both conductors, but you're only required to disconnect ungrounded conductor(s). The neutral may be opened as long as ungrounded conductor(s) also open. Grounded conductor must not be fused.
 