Throw in large junction boxes, wireways, switchboards, panels, trenches, etc. and you can see that there are many inconsistencies in the way this is written. IMO it needs a re-write. :happyyes:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Aux gutters and wireways do not require derating for number of conductors if there are not more than 30 current carrying conductors. They also have a 20 percent fill requirement where raceways is 40 percent fill.

Where wiring space in a panelboard is used as a wireway pretty much same rules apply.

Can you call the space in the panelboard the same as a wireway? Maybe not. There are some similarities though.

There is no doubt an issue here or there could be. As Bob stated there would be a rare or perhaps unusual situation where it may affect the wiring.

I think the nec could be clearer but I bet it won't touch this issue unless the conductors are clearly bundled.

With the new code we now have panels that re 60 circuits with a possibility of 120 CCC..................:eek: What a mess that could be.
 