Page 1 of 2 12 LastLast
Results 1 to 10 of 13
Thread: Meter pan after service disconnect
  1. #1
    Join Date
    Jun 2005
    Jersey Shore
    Posts
    422
    Looked at a service the other day, the meter was located after the service disconnect. The grounded conductor was never bonded to the service disconnect enclosure, it was passed through into the meter enclosure where it was bonded to the meter enclosure and a #8 bonding jumper was brought back to the service disconnect for bonding. I'm ordering a ground lug kit for the disconnect, however how do I handle the meter enclosure? I don't know if there is a way to separate the equipment grounds and neutrals at the meter enclosure. PVC was used between meter and service enclosures.
  2. #2
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,565
    Quote Originally Posted by Ken9876 View Post
    That disconnect may be required by the POCO and if so, it wouldn't be treated the same as the service disconnect required under the NEC.
    If you aim at nothing, you will hit it every time!
  3. #3
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    2,491
    Quote Originally Posted by Little Bill View Post
    That is what I was thinking. Progress Energy does that in this area. The "disconnect" is part of the Utlity Company equipment and it is not fused or otherwise amperage rated. The Service Disconnect is still the first means of disconnect on the load side of the meter.
    I know what I don't know, and I know where to go to find it!
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,273
    So the question to the OP is whether or not there is a "service disconnect" on the load side of the meter?
  5. #5
    Join Date
    Jun 2005
    Jersey Shore
    Posts
    422
    The disconnect before the meter is fused. The conductors then enter the meter, where the equipment grounding conductor originates. From the meter they run 500' to a remote structure to a breaker at the remote structure.
  6. #6
    Join Date
    Jan 2007
    Posts
    3,444
    The Power Company here requires a disconnect ahead of the meter on 480v Services Only.
    This is not considered the "Service Disconnect".
    Only a Safety Switch they can shut off so they can Safely pull or service the Meter.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,273
    250.142(B) exception 2 likely allows you to bond the meter enclosure with the grounded conductor, good thing is you said you have non metallic raceway so that prevents the raceway from becoming a parallel path for neutral current.
    Exception No. 2: It shall be permissible to ground meter enclosures by connection to the grounded circuit conductor on the load side of the service disconnect where all of the following conditions apply:
    (1) No service ground-fault protection is installed.
    (2) All meter enclosures are located immediately adjacent to the service disconnecting means.
    (3) The size of the grounded circuit conductor is not smaller than the size specified in Table 250.122 for equipment grounding conductors.
    I have the opinion that the 200 amp disconnect is the service disconnect since it contains overcurrent devices, and the equipment grounding conductors should originate there with the allowed exception in 250.142(B) if it is done in a way there is no objectionable current over metal raceways, enclosures, etc. Is the neutral in this 4 gang meter permanently bonded to the can or is there a jumper, screw, etc. that can be installed/removed as needed? I would isolate neutral in meters if it is easy to do so.
    Keep in mind your grounded conductor as well as the equipment grounding conductor need sized to the 200 amp overcurrent device on the supply side and not the 100 amp device on the load side, or be no larger than the ungrounded conductors if they would happen to be smaller than 250.122 (which should not be a problem in this case).
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,273
    Quote Originally Posted by kwired View Post
    Some of what I said here applies, some of it - I had the content of another thread but similar topic on my mind and did not realize I was replying to a different thread.
    OP in this thread did not mention size of disconnects or the fact it was a 4 gang meter socket, those parts were from a different therad. Sorry for any confusion.
  9. #9
    Join Date
    Jun 2005
    Jersey Shore
    Posts
    422
    Thank you for the info, very helpful
  10. #10
    Join Date
    Jul 2007
    Posts
    3,100
    Cold sequence metering, usually 400 amp 480 volt services, mainly a poco requirement to make it safer for their meter guys and gals.