Originally Posted by
Smart $
OP'er simply wants to know if a multi-pole contactor rating of 30A means 30A per pole or 30A total.
And what would be the difference between the two?
In what context does the word "total" come into play here? If you put two lights in parallel, with one drawing 1 amp and the other drawing 2 amps, then the two lights draw a "total" of 3 amps. But if you individually measure the amps flowing in each of the two poles of a 2-pole contactor, and if your meter gives you a reading of 15 amps in each case, are you going to conclude that the contactor is experiencing a "total" current of 30 amps? I hope not. This is not an "amps plus amps equals amps" situation. It is an "amps flowing out equal amps returning" situation.
Charles E. Beck, P.E., Seattle
Comments based on 2008 NEC unless otherwise noted.