Thread: Are lug's code compliant on this DIY 175A breaker panel? Needed for 10KW PV system

  1. #21
    Join Date
    May 2011
    Posts
    773
    Quote Originally Posted by Smart $ View Post
    For a 10kW max system, a 60A disconnect fused at 45A or a 45A MCCB would suffice. Other details would present themselves, such as where and how to tap the service conductors.
    If the system is 10kW AC at 240V, it will require a 60A OCPD, due to PV being considered a continuous load.

    Quote Originally Posted by superduperenergydude View Post
    Unfortuantely AHJ does not permit line side taps for residential.
    That is such BS. Do they allow it for the other purposes explicitly permitted by the NEC? AHJs need to get over it. I realize my saying all this doesn't help you.

    I thought this would be a very common situation with a common solution? I guess not.
    Yeah, the common solution is the line side tap! Or the breaker downsizing.

    There are a lot of 200A homes out there. Do most of you PV installers just recommend 7.1KW max systems so you dont' have to mess with this?
    I think most installers would try to present two options, the one that requires the upgrade and the one that does not. And do their homework on the supply-side connection option before giving the quote.

    Quote Originally Posted by don_resqcapt19 View Post
    I would install a 200 amp fusible disconnect with 175 amp fuses as the service disconnect and connect the load side of the new disconnect to the line side of the 200 amp breaker in the panel. You will also have to relocate the main bonding jumper to the new disconnect and separate the EGCs and neutrals at the existing panel.
    This would probably be the cheapest, simplest solution, if the AHJ won't allow a supply side connection.

  2. #22
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    9,526
    Quote Originally Posted by jaggedben View Post
    Quote Originally Posted by Smart $
    For a 10kW max system, a 60A disconnect fused at 45A or a 45A MCCB would suffice. Other details would present themselves, such as where and how to tap the service conductors.
    If the system is 10kW AC at 240V, it will require a 60A OCPD, due to PV being considered a continuous load.
    I realized that after I posted, but also after OP'er replied saying AHJ doesn't permit line-side taps. Figured correcting my statement wasn't worth bothering.

    That is such BS. ... AHJs need to get over it. I realize my saying all this doesn't help you.

    Yeah, the common solution is the line side tap! ...
    My sentiments exactly.
    Whomever says or otherwise portrays "I am there" is a liar.

  3. #23
    Join Date
    Sep 2008
    Location
    Fairmont, WV, USA
    Posts
    740
    Quote Originally Posted by George Stolz View Post
    Sounds like a good reason to go to the supply house before wasting time chasing basic parts on Google.
    The guy at my supply house can get me virtually any breaker of any make up to 600A & 600V within a week, often within 48 hours.

  4. #24
    Join Date
    Jan 2012
    Location
    CA
    Posts
    125
    superduperdude,

    If i consider the fundamental problem to be how to connect a 10 kw pv system to a 200 Amp panel with minimum expense - and in a Code-compliant fashion:

    Pls. consider a 8 KW inverter. If made by SMA (good idea in any case) its cont. rated AC current is actually only 32A. (It should be 33.333)
    That was specifically done to allow use of a 40A brkr. (not 45, 50 or 60)
    40 A vs 200 A Main = 120% rule met.

    True, 10 kw pv array vs an 8 kw inverter is on the high side for pv array to inverter ratio.
    BUt install 9.6 KW of panels.
    That gives you a 1.2 ratio. In my area that is the upper limit of good system design.
    It is, however, an excellent option for 10 KW of DC power on a 200 A main.
    Hell, considering that usually you will see 2/3 of the dc rating in output, you can even put in 10 KW.

    1. Code does not prevent you.
    2. Real world doesn't either: On those rare days and moments that the pv is capable of more power than the inverter, the inverter will just clip it to max 32 A. No danger of overload.

    (ps you didn't ask, and you probably know, but ensure PV breaker is landed opposite feed in Main
    Both Code, and safety considerations, require it

    pss if you really want to be pro, ensure inverter is in shady, cool spot. It will be operating closer to its peak on a more regular basis. It will be hotter more often. Heat is a major inverter killer. Fans or no. Fans can and do fail on these guys, to boot.)

    If, on the other hand, you meant 10 kw AC system, then...... what those guys said! :-))

  5. #25
    Join Date
    Sep 2012
    Location
    york, sc
    Posts
    11
    "ensure PV breaker is landed opposite feed in Main
    Both Code, and safety considerations, require it"

    Yes the inverters are going to be inside and breakers located very far away from main panel in a sub panel.

  6. #26
    Join Date
    May 2011
    Posts
    773
    Quote Originally Posted by superduperenergydude View Post
    "ensure PV breaker is landed opposite feed in Main
    Both Code, and safety considerations, require it"

    Yes the inverters are going to be inside and breakers located very far away from main panel in a sub panel.
    Regardless of whether the breakers are located in a subpanel, the PV backfeed needs to be located opposite the main feed in all panels. See 705.12(D)(7).

  7. #27
    Join Date
    Sep 2012
    Location
    york, sc
    Posts
    11

    qrn vs qn breakers

    So the exsisting main breaker is a siemens/ITE qrn series 200amp
    a guy i called said there is a ITE qn2175 breaker that would work
    however looking the data sheet below, it looks like qrn are horizontal and qn series are vertical.
    However, when you look at the product names on this same data sheet there are NONE named qrn. that's confusing. does anyone know differences between qrn and qn series?

    http://w3.usa.siemens.com/powerdistr...01-038-039.pdf

  8. #28
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    9,526
    Quote Originally Posted by superduperenergydude View Post
    So the exsisting main breaker is a siemens/ITE qrn series 200amp
    a guy i called said there is a ITE qn2175 breaker that would work
    however looking the data sheet below, it looks like qrn are horizontal and qn series are vertical.
    However, when you look at the product names on this same data sheet there are NONE named qrn. that's confusing. does anyone know differences between qrn and qn series?

    http://w3.usa.siemens.com/powerdistr...01-038-039.pdf
    As noted...
    [Note 5] QNR required for horizontal applications or vertical
    applications where the lugs are facing up. The QN
    breaker is required for vertical applications where the
    lugs are facing down as shown.
    Whomever says or otherwise portrays "I am there" is a liar.

  9. #29
    Join Date
    Sep 2012
    Location
    york, sc
    Posts
    11
    " Originally Posted by George StolzSounds like a good reason to go to the supply house before wasting time chasing basic parts on Google.
    The guy at my supply house can get me virtually any breaker of any make up to 600A & 600V within a week, often within 48 hours."

    I went to 4 supply houses before someone who had been working in the trade for years came up with almost the exact part I needed. NONE of the 4 supply houses knew of 175amp siemens breaker. Had 3 of them tell me it didnot exsist. The GE breaker 175A was also not available until I pulled it out of my box and showed them.
    ONE place even sold sunny boy and solar panels.

    And in the end it was me searching the internet getting the exact part number that I needed and telling the supply store what to order. qn2175R

    the "r" at the end of the nomenclature is what confused me.

    I appreciate the help on the forum none the less.

    so basically the advice you give is only good if you have knowledgeable sellers.

    I probably took 10 hours or more finding this solution, but popping out a breaker and putting in a new one will be easy and obvioulsy be code compliant.
    Last edited by superduperenergydude; 09-13-12 at 11:22 AM.

  10. #30
    Join Date
    Jun 2005
    Location
    Delmarva, USA
    Posts
    1,549
    Quote Originally Posted by George Stolz View Post
    Sounds like a good reason to go to the supply house before wasting time chasing basic parts on Google.
    In my experience these days, I can find it quicker, get it quicker and for less $$$ than the supply houses.

    Case in point:

    I needed a EHB24020 breaker. None of the supply houses had one. One of them said they could get it from a broker. For about $400. Rest of`em said SOL.

    I found one brand new on ebay for less than $150. Took 2 days to get it here. `Nuff said.