Originally Posted by
jaggedben

Originally Posted by
Smart $
For a 10kW max system, a 60A disconnect fused at 45A or a 45A MCCB would suffice. Other details would present themselves, such as where and how to tap the service conductors.
If the system is 10kW AC at 240V, it will require a 60A OCPD, due to PV being considered a continuous load.
I realized that after I posted, but also after OP'er replied saying AHJ doesn't permit line-side taps. Figured correcting my statement wasn't worth bothering.
That is such BS. ... AHJs need to get over it. I realize my saying all this doesn't help you.
Yeah, the common solution is the line side tap! ...
My sentiments exactly.
Whomever says or otherwise portrays "I am there" is a liar.