    service

    going to run new service underground to new garage 120/240 single phase.going to use URD direct buried wire . I know in need sch 80 pvc and expansion joint at meter and minium 18 inches in ground but should i 90degree pipe in ground or just straight?

  2. #2
    Join Date
    Feb 2006
    Location
    Memphis, TN
    Posts
    565
    Quote Originally Posted by jim123 View Post
    going to run new service underground to new garage 120/240 single phase.going to use URD direct buried wire . I know in need sch 80 pvc and expansion joint at meter and minium 18 inches in ground but should i 90degree pipe in ground or just straight?
    IMO Straight would suffice.
    Rick. Shelby county TN. 2002 code cycle.

  3. #3
    Join Date
    Jul 2005
    Location
    northern new jersey
    Posts
    194
    Straight with a bushing or 90, But check with your power company!
    Their web site should have requirements
    just something to look at.
    http://www.rizzcon.com/index.html

  4. #4
    Join Date
    Jul 2007
    Posts
    3,100
    Our local POCO requires a 90 and 3" conduit in their specs for a 200 amp service, but they don't enforce it.