Table 300.5 question

Status
Not open for further replies.

GerryB

Senior Member
Does table 300.5, minimum cover requirements, include interior work such as chiseling a chase for a floor outlet. Would you still need 2" of concrete over pvc in that case. If not how much?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No, that table is for underground work not a raceway embedded in concrete.

300.5 Underground Installations.
(A) Minimum Cover Requirements. Direct-buried cable
or conduit or other raceways shall be installed to meet the
minimum cover requirements of Table 300.5.
 