extruder lockout/estop

Status
Not open for further replies.
I work in a plant doing polymer extrusion.

Recently an insurance guy was walking through the plant and noticed the way we lock out the machines to clean them.

there is no real way to get a hand stuck in the extruder screw.

What are your thoughts as to whether or not this meets minimum requirements?

Should there be knife switch or contactor means of disconnect?

this is an example estop.jpg
20190225_125322.jpg
 

kwired

Electron manager
Location
NE Nebraska
Locking out that control switch still leaves some possibility of the motor unexpectedly starting. Should something crush the control circuit cable and short the two main control leads together the drive will see that as a run command.

Opening the drive supply conductors or even the motor conductors with something that will not close (and then locking it open) is much more reliable at preventing that motor from unexpectedly starting from a safety perspective.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Locking out that control switch still leaves some possibility of the motor unexpectedly starting. Should something crush the control circuit cable and short the two main control leads together the drive will see that as a run command.

Opening the drive supply conductors or even the motor conductors with something that will not close (and then locking it open) is much more reliable at preventing that motor from unexpectedly starting from a safety perspective.
Or a single failure in the drive itself, for that matter.
NEC and OSHA may have slightly different rules on disconnects when intended only for mechanical maintenance. For electrical work that circuit would not count.
 

kwired

Electron manager
Location
NE Nebraska
Or a single failure in the drive itself, for that matter.
NEC and OSHA may have slightly different rules on disconnects when intended only for mechanical maintenance. For electrical work that circuit would not count.
OP's question is mostly about clean out of the equipment, so lockout in question is mostly about mechanical lockout. If the breaker/disconnect supplying the drive is capable of being locked that may be just fine for the insurance inspector mentioned in the OP.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A device that does not open the power conductors is never suitable for use as a disconnect or a lockout.
 
contactor

contactor

Here is language from OSHA.

Energy isolating device. A mechanical device that physically prevents the transmission or release of energy, including but not limited to the following: A manually operated electrical circuit breaker; a disconnect switch; a manually operated switch by which the conductors of a circuit can be disconnected from all ungrounded supply conductors, and, in addition, no pole can be operated independently; a line valve; a block; and any similar device used to block or isolate energy. Push buttons, selector switches and other control circuit type devices are not energy isolating devices.

-------------------------------------------------------------

from what i read here. using this type of switch along with a contactor, removing power from the line side of the drive should meet requirements
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
I work in a plant doing polymer extrusion.

Recently an insurance guy was walking through the plant and noticed the way we lock out the machines to clean them.

there is no real way to get a hand stuck in the extruder screw.

What are your thoughts as to whether or not this meets minimum requirements?

Should there be knife switch or contactor means of disconnect?

this is an example View attachment 22415
View attachment 22414

We wouldn't get by with anything less than a padlocked off input isolator and LOTO.
Lock off, tag off.
And that's just a British way of doing things. We were owned by one of the major US electrical giants.
 

cpickett

Senior Member
Location
Western Maryland
Occupation
Electrical Engineer
If I was doing this install, I would put a lockable disconnect at the motor, to open the motor leads, and put aux contacts in the disconnect wired to your stop circuit. That way, when the disconnect is open, the drive can't start. The disconnect satisfies LOTO, and prevents the motor from running, and the aux contacts protect the drive if it tries to start with no load (motor) connected.

Also, if you are using an Allen Bradley drive that has safe torque off (STO) inputs, use those for your e-stop, not the stop input. Other brands have similiar features. That will provide a safety rated way to stop the drive when the e-stop is pushed. Also, it will disconnect power to the motor right away, versus the stop input that may have a ramp time programmed.
 

kwired

Electron manager
Location
NE Nebraska
If I was doing this install, I would put a lockable disconnect at the motor, to open the motor leads, and put aux contacts in the disconnect wired to your stop circuit. That way, when the disconnect is open, the drive can't start. The disconnect satisfies LOTO, and prevents the motor from running, and the aux contacts protect the drive if it tries to start with no load (motor) connected.

Also, if you are using an Allen Bradley drive that has safe torque off (STO) inputs, use those for your e-stop, not the stop input. Other brands have similiar features. That will provide a safety rated way to stop the drive when the e-stop is pushed. Also, it will disconnect power to the motor right away, versus the stop input that may have a ramp time programmed.
From user safety perspective the aux contact doesn't matter - those are installed to protect the drive, more so to protect from closing the switch when the drive has an active output which can be hard on the drive and not so much of a problem of opening the output circuit when it is active, especially on the drives we see these days, older drives this was even bigger deal to make sure that aux contact opened before the power conductors opened.
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
If I was doing this install, I would put a lockable disconnect at the motor, to open the motor leads, and put aux contacts in the disconnect wired to your stop circuit. That way, when the disconnect is open, the drive can't start. The disconnect satisfies LOTO, and prevents the motor from running, and the aux contacts protect the drive if it tries to start with no load (motor) connected.
Why not on the input supply to the VFD? Wouldn't that be simpler/more effective?
 

cpickett

Senior Member
Location
Western Maryland
Occupation
Electrical Engineer
Why not on the input supply to the VFD? Wouldn't that be simpler/more effective?

I usually figure on the drive being in a cabinet somewhere else and if you put the disconnect near the motor being serviced, you won't have to run your power leads back and forth. As Kwired mentioned, the aux contacts provide no safety benefit but if it saves a drive, or prevents opening or closing the disconnect under load, it's cheap insurance in my book.
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
I usually figure on the drive being in a cabinet somewhere else and if you put the disconnect near the motor being serviced, you won't have to run your power leads back and forth. As Kwired mentioned, the aux contacts provide no safety benefit but if it saves a drive, or prevents opening or closing the disconnect under load, it's cheap insurance in my book.
No running back and forth of power cables. The normal arrangement for the installations is a 3-phase supply to the drive and a 3-phase supply from the drive to the motor. The input to the drive got locked off, tagged off, padlocked. Usually there was a device so that multiple padlocks could be attached. The guy(s) working on the motor or driven plant would have their own keys.

I carried my own set of padlocks. As did my guys.
Just the way we did it.
 

kwired

Electron manager
Location
NE Nebraska
No running back and forth of power cables. The normal arrangement for the installations is a 3-phase supply to the drive and a 3-phase supply from the drive to the motor. The input to the drive got locked off, tagged off, padlocked. Usually there was a device so that multiple padlocks could be attached. The guy(s) working on the motor or driven plant would have their own keys.

I carried my own set of padlocks. As did my guys.
Just the way we did it.
lock with multiple padlocks for each worker is common thing and basically what OSHA would like to see as a general rule.

The issue is NEC calls for a disconnect within sight of the motor, though when there is a VFD it potentially can trigger an exception to that rule, but the fact that one can put an aux contact in the disconnect to switch the VFD control circuit kind of eliminates any impracticality issue that triggers the exception.
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
lock with multiple padlocks for each worker is common thing and basically what OSHA would like to see as a general rule.

The issue is NEC calls for a disconnect within sight of the motor, though when there is a VFD it potentially can trigger an exception to that rule, but the fact that one can put an aux contact in the disconnect to switch the VFD control circuit kind of eliminates any impracticality issue that triggers the exception.
We have done that too, the line of sight disconnect. Just isolators not rated to make or break load current. But then you have auxiliaries like cooling fans, anti-condensation heaters. winding thermistors, and etc.
 

kwired

Electron manager
Location
NE Nebraska
We have done that too, the line of sight disconnect. Just isolators not rated to make or break load current. But then you have auxiliaries like cooling fans, anti-condensation heaters. winding thermistors, and etc.
Many those auxiliaries the NEC doesn't require disconnect to be within sight, but motors over 300VA or 1/8 HP it does.
 