Results 1 to 9 of 9
Thread: Single Phase Neutral Sizing
  1. #1
    Join Date
    Mar 2012
    Minneapolis, MN
    Posts
    241
    What should be the size of grounded (neutral) conductor in a 120/240V 3-wire single phase system as per NEC?
    The 3-wire single phase system has one grounded (neutral) conductor and two ungrounded conductors. The one grounded (neutral) conductor carries current from both ungrounded conductors. So apparently the size of grounded (neutral) conductor should be twice as big as each ungrounded conductor; is it correct?
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    17,083
    Quote Originally Posted by timm333 View Post
    See 220.61
    Barring additive harmonics, (not a problem in single phase) the current in the ungrounded conductors would cancel not add.
    Roger
    Join Date
    Mar 2012
    Minneapolis, MN
    Posts
    241
    I thought current in ungrounded conductor cancelled out only in three phase systems. Does current also cancel out in single phase 3-wire system?
  4. #4
    Join Date
    Feb 2003
    Illinois
    Posts
    23,542
    Yes it cancles in a single phase 3 wire system. It does not cancel in a 3 wire system that is derived from two ungrounded conductors and a grounded conductor from a 3 phase wye system.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  5. #5
    Join Date
    Mar 2012
    Minneapolis, MN
    Posts
    241
    So should the size of neutral/grounded conductor be the same as the size of each of the two ungrounded conductors in single phase 3-wire system? Or should the size of neutral/grounded conductor be bigger than the size of each of the two ungrounded conductors?
  6. #6
    Join Date
    Feb 2003
    Fl
    Posts
    17,083
    Did you look at 220.61?
    Roger
    Join Date
    Mar 2012
    Minneapolis, MN
    Posts
    241
    Yes I checked NEC 220.61. It says that size neutral conductor equal to one of the phase conductors. But for 2-phase 3-wire system, size neutral equal to 140% of one of the phase conductors. This means that for our 120/240V 1-phse system, neutral conductor will be sized equal to one of the phase conductors.
    The only thing I want to be sure is that 120/240V system is really a 1-phase system (and is not a 2-phase system.) 120/240V 1-phase system has two phase conductors and one neutral, and the 2-phase system also has two phase conductors and one neutral. So what is the difference between these two systems? Thanks for help!
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,958
    Yes 120/240 is a 1 system. A 2 system is a nearly obsolete, completely different animal.
    Rob
  9. #9
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    For a 120/240V 1 3W system, using the neutral as a common reference, the ungrounded conductor's voltages are 180 out of phase.
    For a 120V 2 3W system, using the grounded conductor as a common reference, the ungrounded conductor's voltages are 90 out of phase (could also be 270, depending on which is used as the reference voltage). The grounded conductor currents partially cancel out, which is the reason for the 140%.
    I will have achieved my life's goal if I die with a smile on my face.
  10. #10
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Yes I checked NEC 220.61. It says that size neutral conductor equal to one of the phase conductors. ... This means that for our 120/240V 1-phse system, neutral conductor will be sized equal to one of the phase conductors.
    That's not really what it says... but you can size it the same as the ungrounded. What it does say is that it can be smaller, depending on the loads. On a 120/240 1 3W system, there may be line-to-loads loads which will not contribute any neutral current. As such, the neutral size can be reduced by this amount per calculation (effectively the compliment of sizing to maximum unbalanced neutral current).