NEC 2017 207.12 (B)(2)(3)(a)

Status
Not open for further replies.

thamessolar

Member
Location
Denver, Co
Can you give me your opinion of which of the following methods you agree with? Our state inspector uses you as a reference for requiring method two.
Question: Is the 100 amp busbar in the garage panel adequate or does the code require it to be increased to 200 amps?


Method one – My understanding using NEC 2017 705.12(B)(2)(3)(a) – 125% of the inverter output current rating plus the utility fed main breaker does not exceed the busbar rating.
20.96A x 1.25 = 26.20A +50A main = 76.2A < 100 busbar.
Therefore, the existing 100a garage panel is adequate.

Method two – Colorado State Electrical inspectors understanding of the NEC. The code requires that the size of the breaker being backfed by a PV inverter onto a panel busbar does not exceed 20% of the busbar rating
200A busbar x 20% = 40A backfed breaker
Therefore, the panel busbar must be increased to 200 amps.
 