hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch has incoming utility transformer service conductor to pole where service conductors split to weather head masts P1 to P4. Two views are shown Front View and Side View. Building has four tenant. There is tenant #1 first floor has basement also belong to tenant #1. Same deal with tenant #2 to tenant #4 with basement #2 to basement #4 belong to each respective tenant.
Per NEC 2014 230.40 exception no.1 I can have one set of overhead services to each occupancy. So P1 to P3 each have one set of overhead service conductors to tenants as shown on attached sketch.
However, P4 Side View has conductors on roof to opposite side, go downoutside wall building then half way down into the building common area basement.
So is common area occupancy? Question is does P4 installation comply per Nec 2014 Article 240.40 exception no. 1?
Sent from my SM-G935U using Tapatalk
Per NEC 2014 230.40 exception no.1 I can have one set of overhead services to each occupancy. So P1 to P3 each have one set of overhead service conductors to tenants as shown on attached sketch.
However, P4 Side View has conductors on roof to opposite side, go downoutside wall building then half way down into the building common area basement.
So is common area occupancy? Question is does P4 installation comply per Nec 2014 Article 240.40 exception no. 1?
Sent from my SM-G935U using Tapatalk