Tenant panel and one branch ckt

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch I have on first floor four tenant spaces in office building with four stories. The Panel G from which four tenants branch circuits are fed out of is in common area electric room. Typically you have one subpanel for each tenant feeding branch circuits however in my case their is one Panel G in common area electric room. The keys to the electric room are given to each tenant. Branch circuits for power for each tenant is fed from Panel G.

However, all lights for all four tenants are fed from one branch circuit breaker in Panel G.

The questions are:

1. Is one branch circuit breaker for light for all tenant against code?

2. Would giving the keys to each tenant make installation compliant with NEC 2014 Article 240.24(B) even though the panel is located in electric room common area?
0728424c60ab9bd868d51a5ff521063b.jpg


Sent from my SM-G935U using Tapatalk
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Attached sketch I have on first floor four tenant spaces in office building with four stories. The Panel G from which four tenants branch circuits are fed out of is in common area electric room. Typically you have one subpanel for each tenant feeding branch circuits however in my case their is one Panel G in common area electric room. The keys to the electric room are given to each tenant. Branch circuits for power for each tenant is fed from Panel G.

However, all lights for all four tenants are fed from one branch circuit breaker in Panel G.

The questions are:

1. Is one branch circuit breaker for light for all tenant against code?

2. Would giving the keys to each tenant make installation compliant with NEC 2014 Article 240.24(B) even though the panel is located in electric room common area?

Sent from my SM-G935U using Tapatalk

1. Yes.
2. No.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I will have to disagree with gadfly56.

My answer to #2 is "Yes." I don't like the notion, but it does fit in with the way article 240.24(B) is worded. Nothing says that a tenant has to be the only one who has access to their branch circuit breakers.

I think #1 is trickier than it may appear, on the surface, to be. The relevant rule is 210.25(B). I believe its intent is to say that a panel located in tenant space A cannot power lights in other tenant spaces or in common areas. But that is not what is happening here. The actual words are (edited to remove words not relevant to this issue), ". . . circuits installed for . . . lighting . . . for . . . common areas of . . . a multi-occupancy building shall not be supplied from equipment that supplies an individual . . . tenant space." You don't have "equipment that supplies an individual tenant space." Rather, you have a single piece of equipment that supplies all tenant spaces. Bottom line, my answer to #1 is "No."
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I will have to disagree with gadfly56.

My answer to #2 is "Yes." I don't like the notion, but it does fit in with the way article 240.24(B) is worded. Nothing says that a tenant has to be the only one who has access to their branch circuit breakers.

I think #1 is trickier than it may appear, on the surface, to be. The relevant rule is 210.25(B). I believe its intent is to say that a panel located in tenant space A cannot power lights in other tenant spaces or in common areas. But that is not what is happening here. The actual words are (edited to remove words not relevant to this issue), ". . . circuits installed for . . . lighting . . . for . . . common areas of . . . a multi-occupancy building shall not be supplied from equipment that supplies an individual . . . tenant space." You don't have "equipment that supplies an individual tenant space." Rather, you have a single piece of equipment that supplies all tenant spaces. Bottom line, my answer to #1 is "No."

I'd suggest the relevant rule is 210.25(A):

210.25 Branch Circuits in Buildings with More Than
One Occupancy.


(A) Dwelling Unit Branch Circuits. Branch circuits in
each dwelling unit shall supply only loads within that dwelling
unit
or loads associated only with that dwelling unit.

The lighting circuit in any dwelling is certainly a branch circuit, it certainly supplies loads, and it is certainly supplying more than one dwelling unit once it leaves the first dwelling unit it serves.

I'll geek to changing the answer to #2 to a "yes".
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I'd suggest the relevant rule is 210.25(A):

210.25 Branch Circuits in Buildings with More Than
One Occupancy.


(A) Dwelling Unit Branch Circuits. Branch circuits in
each dwelling unit shall supply only loads within that dwelling
unit
or loads associated only with that dwelling unit.

The lighting circuit in any dwelling is certainly a branch circuit, it certainly supplies loads, and it is certainly supplying more than one dwelling unit once it leaves the first dwelling unit it serves.

I'll geek to changing the answer to #2 to a "yes".
What I have is not dewelling unit but commericial office space.

Sent from my SM-G935U using Tapatalk
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
What I have is not dewelling unit but commericial office space.

Sent from my SM-G935U using Tapatalk

Ahhhhh, when you said "tenant" I automatically thought "dwelling unit". :slaphead: In that case, I'll change my "no" to a "yes".
 