As far as industry can bus drop be used on a permanent install? I was told at one time it was up to the authority have jurisdiction at the plant you worked in. What kind of codes do we have for it, I can find very little about this.
 

beenther1s

Member
Location
Fort Wayne
No, I am asking about 480 3 phase hook up to say CNC machines. I have heard that it can only be used as temporary wiring. In most cases though they are talking about SO cord
 

iwire

Moderator
Staff member
Location
Massachusetts
Check it out


368.56 Branches from Busways. Branches from busways
shall be permitted to be made in accordance with
368.56(A), (B), and (C).

(B) Cord and Cable Assemblies. Suitable cord and cable
assemblies approved for extra-hard usage or hard usage and
listed bus drop cable shall be permitted as branches from
busways for the connection of portable equipment or the
connection of stationary equipment to facilitate their interchange
in accordance with 400.7 and 400.8 and the following
conditions:

(1) The cord or cable shall be attached to the building by
an approved means.

(2) The length of the cord or cable from a busway plug-in
device to a suitable tension take-up support device shall
not exceed 1.8 m (6 ft).

(3) The cord and cable shall be installed as a vertical riser
from the tension take-up support device to the equipment
served.

(4) Strain relief cable grips shall be provided for the cord
or cable at the busway plug-in device and equipment
terminations.

Exception to (B)(2): In industrial establishments only,
where the conditions of maintenance and supervision ensure
that only qualified persons service the installation,
lengths exceeding 1.8 m (6 ft) shall be permitted between
the busway plug-in device and the tension take-up support
device where the cord or cable is supported at intervals not
exceeding 2.5 m (8 ft).
 

beenther1s

Member
Location
Fort Wayne
accordance with 400.7 and 400.8 and the following
conditions:


That is the kicker, it says in 400.7 (7) Connection of utilization equipment to facilitate frequent interchanges (8) for ready removal
Nowhere can I find you can wire this as a permanent

400.8 Says it can not be used as fixed wiring of a struture

So is it all talking about busdrop or is busdrop its own entity

...and yes it is supplied from a bus bar with a disconnect
 

iwire

Moderator
Staff member
Location
Massachusetts
accordance with 400.7 and 400.8 and the following
conditions:


That is the kicker, it says in 400.7 (7) Connection of utilization equipment to facilitate frequent interchanges (8) for ready removal
Nowhere can I find you can wire this as a permanent

400.8 Says it can not be used as fixed wiring of a struture

So is it all talking about busdrop or is busdrop its own entity

...and yes it is supplied from a bus bar with a disconnect

368.56 allows it, it is common and no special permission is required.

I guess you did not see the exception under 400.7(B) or notice 400.7(A)(1)
 