Page 1 of 2 12 LastLast
Results 1 to 10 of 11
Thread: shunt trip for elevators
  1. #1
    Join Date
    Sep 2011
    wisconsin
    Posts
    213
    Is there any code that states I cant run the 2 #12 wires for the shunt trip in the same conduit as the feeder for that elevator car???
  2. #2
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,474
    Quote Originally Posted by copper chopper View Post
    Don't have it handy, but mixing Class 1 and Class 2/3 circuits in the same raceway is a no-no IIRC.
  3. #3
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    The derating required for over 3 current carrying conductors will reduce the ampacity of the feeder.
    It makes no sense but I don't see any exceptions to get around it.
    Gadfly, the shut trip would not be class 2 or3.
  4. #4
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,474
    Quote Originally Posted by iwire View Post
    It is if it's operating off a 24 volt coil. Actually, I assumed that the pair he's talking about was running from the addressable relay module back to the elevator controller, which I admit may not be what he was saying.
  5. #5
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by gadfly56 View Post
    The only shunt trip breakers I have installed have all had 120 VAC trip coils.
    We would be running that 120 VAC through an addressable fire alarm relay.
  6. #6
    Join Date
    Sep 2008
    Fairmont, WV, USA
    Posts
    2,073
    NO derating required
    725.51(B)(2)
  7. #7
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by fmtjfw View Post
    725.51(B)(2)
    2011 NEC
    725.51(B)(2)
    (B) Power-Supply Conductors and Class 1 Circuit Conductors.
    Where power-supply conductors and Class 1 circuit
    conductors are permitted in a raceway in accordance
    with 725.48, the number of conductors shall be determined
    in accordance with 300.17. The ampacity adjustment factors
    given in 310.15(B)(3)(a) shall apply as follows:
    (2) To the power-supply conductors only, where the Class
    1 circuit conductors do not carry continuous loads in
    excess of 10 percent of the ampacity of each conductor
    and where the number of power-supply conductors is
    more than three
    Thanks.
  8. #8
    Join Date
    Feb 2003
    Illinois
    Posts
    23,465
    It is if it's operating off a 24 volt coil. ...
    Maybe not. Just because it is a 24 volt system does not automatically mean that it is a class 2 system. It is only a class 2 system if the power supply is a listed class 2 power supply.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  9. #9
    Join Date
    Sep 2011
    wisconsin
    Posts
    213
    thank you iwire and you are correct it is 120 volt coils . so I will pull them in with the feeder, this saves me about 200 feet of 1/2" conduit and labor to install it...
  10. #10
    Join Date
    Sep 2008
    Fairmont, WV, USA
    Posts
    2,073
    2011 NEC
    Thanks.
    I put that every year on the WV SkillsUSA Motor Controls test written part. It's in an article lots of people never look at. As the OP said, it can save you time and money.