    Exterior emergency egress lighting??

    I have a set of plans that call for Exterior emergency egress lighting??

    Next day electical supply house does not have a clue(nor do I)

    What does it look like?? Where can I get 2?.......

    Do any other cities require these in building/remodeling permits???


    Thank you
    Dennis

  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    6,449
    Quote Originally Posted by rt66electric View Post
    I have a set of plans that call for Exterior emergency egress lighting??

    Next day electical supply house does not have a clue(nor do I)

    What does it look like?? Where can I get 2?.......

    Do any other cities require these in building/remodeling permits???


    Thank you
    Dennis
    For buildings which under the Fire code are required to have emergency egress lighting in the first place, the lighting requirement does not just cover the inside of the building but includes the exterior paths or routes to some public right of way or place of safety. Sounds like the plans are referring to that.
    Your problem is that that lighting has to be engineered to provide the required light levels from one end to the other rather than just being provided by a named fixture.
    Whoever drew up the plans apparently left that responsibility to you, or else the details are in another document.

  3. #3
    Join Date
    Dec 2008
    Location
    Oklahoma
    Posts
    446

    where do you get one?

    I guess I have never noticed an outdoor module. Who is a supplier??

  4. #4
    Join Date
    Jan 2011
    Posts
    412
    First off, what is your normal exterior light source? What type of fixture(s)?


    Often what is done is an interior battery back up exit sign (usually by the exit) with a remote exterior head. Of course the sign has to be rated for the remote head. Another possibility is a fluorescent/LED fixture with a battery back up ballast built in. A 3rd would be a UPS in the electrical closet for the cuircuits running the exterior lights.

    Fire and local code will dictate how many lumens per foot and if the run time needs to be above 90minutes.

  5. #5
    Join Date
    Feb 2003
    Location
    Huntsville Alabama
    Posts
    2,000
    One of these

    http://www.e-conolight.com/exit-emer...xhs0906ww.html


    connected to one of these at each exit is usually good enough around here.

    http://www.e-conolight.com/exit-emer...xmdrb2rcw.html



    Special conditions do apply but not very often.
    Some people are like slinkies. They serve absolutely no useful purpose. But still put a smile on your face when pushed down a flight of stairs.

  6. #6
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    6,449
    Quote Originally Posted by masterinbama View Post
    Your remote head is listed for wet locations, but the recommended application is indoors. I wonder who wrote the web page?
    Applications: For general purpose emergency lighting in indoor commercial, retail or industrial applications

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    16,573
    Quote Originally Posted by GoldDigger View Post
    Your remote head is listed for wet locations, but the recommended application is indoors. I wonder who wrote the web page?
    I find errors all the time in the information on web pages, you kind of have to hope that if you download spec sheets that they will have more accuracy to them, but even those are not always accurate. If the people writing the information know little or nothing about the product, then you can not expect them to recognize inaccurate information they are using and to correct it.

  8. #8
    Join Date
    Sep 2004
    Location
    Vancouver, WA
    Posts
    646

    Distance considered safe

    Fire codes require that emergency egress lighting be provided to a distance considered safe. This is especially critical where canopies, railings, or walls outside a building form a barrier to egress. As said above, it is to a place considered public. Battery operated exterior fixtures are needed to provide adequate illumination, typically 1fc average, up to 30ft or more from a building. Concealite makes a type of exterior egress light. Another solution is to provide a central inverter to backup all of the exterior lights on a building. If you use a 277V inverter and one 277V circuit for a bunch of LED or CFL exterior fixtures, you can satisfy the need for egress lighting and emergency egress lighting at the same time.
    e^(i pi) = -1

  9. #9
    Join Date
    Mar 2013
    Location
    North Texas & Georgia
    Posts
    320
    If the fixtures are not speced on the fixture schdule, check with the architect/developer they may want a specific fixture with specific performance metrics.
    As mentioned above, centrally located inverter or UPS are an option using standard fixtures.Exterior/Outdoor emergency fixtures do exist, the following and other lighting manufacturers offer exterior/outdoor emergency fixtures.http://www.google.com/search?num=100...W1MXGB_enUS531

    DualLite/Hubbell
    http://www.dual-lite.com/products/ou...gency_lighting

    Juno
    http://www.junolightinggroup.com/pro...=26592&brand=4

    Lithonia
    http://lithonia.acuitybrands.com/Out...uide/Home.aspx