Results 1 to 7 of 7
Thread: Fluorescent ballast conductor colors
  1. #1
    Join Date
    Nov 2007
    Posts
    869
    I am looking at bidding a job that requires retro fitting approx. 300 4 lamp t-12 troughers to t-8. They are half switched fixtures and will again require 2 ballasts as opposed to (1)4 lamp ballast. In looking at the new electronic ballasts the wiring configuration is different. My question is do the wires leading from the tombstones out into the wiring trough have to correspond (color wise) to the ballast leads? I still need to pull the lampholder brkt out of the fixture, but if I can get away without having to pull out the snap in conductor in the tombstone just to change it's color I will. Was told by the sales person supplying the ballasts to the customer that the new ballasts were a direct replacement and that no wiring change was required.The new electronics have 2 fewer leads. Thanks.
  2. #2
    Join Date
    Sep 2004
    Durham, NC
    Posts
    5,500
    Here is a suppliers web page will multiple listing of the major manufactures of ballast.
    http://www.lightdirectory.com/manufa...gy.php?catid=8
    Hope this helps.
    If you are even thirsty, you are two quarts low.
  3. #3
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,490
    Quote Originally Posted by nizak View Post
    The colors do not have to match. Just make sure you follow the wiring diagram on the ballast.
    Also, the tombstones will have to be shunted. That will also be shown on the wiring diagram.
    Just a note to add, you can get single ballasts to drive 4 lamps.
    If you aim at nothing, you will hit it every time!
  4. #4
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,068
    Quote Originally Posted by Little Bill View Post
    But not to allow you to switch the two pairs on and off independently, which the OP stated was a requirement, to match the currently installed system.
  5. #5
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,490
    Quote Originally Posted by GoldDigger View Post
    Missed that part!
    Rest of my reply still stands though.
  6. #6
    Join Date
    Sep 2008
    Fairmont, WV, USA
    Posts
    2,073
    Actually you can, there are 4 bulb ballasts that have a single power feed and a pilot wire that can be switched to select 2 or 4 bulbs.
    See for instance Diag. 75 (and following diagrams) on page I-35... in http://www.lighting.philips.com/pwc_..._Atlas2012.pdf
    DISCLOSURE: I used to work for Philips Medical and I do own about 1000 shares of Royal Dutch Phillips Electronics.
  7. #7
    Join Date
    Dec 2012
    Posts
    19,068
    Quote Originally Posted by fmtjfw View Post
    That does look handy for retrofit situations. I am particularly fond of the fact that you either leave the sense lead open (off) or connect it to the neutral or any phase wire (on).
Posting Permissions
  • You may not post replies
  • You may not edit your posts