Thread: Grounding/Power Quality Issues

  1. #1
    Join Date
    Dec 2004
    Location
    KY
    Posts
    816

    Grounding/Power Quality Issues

    I have a customer that has come to me and said they are having major transformer overload due to harmonic distortion. We are seeing about 11% Vthd. They have some equipment where they have drilled through the concrete floor and drove a separate ground for the new peice of equipment. They have grounding issue and are tripping and burning up drives like NASCAR tires. This is a large primary user.

    There are many ways to skin this cat. I understand a power quality study should be the first approach in providing a direction. Once this is done, what type of grounding studies are out there that we could have performed to help determine if there are ground loops, high Vthd, high Ithd. I am looking at some line reactors as well but i don't want to get the cart in front of the horse.

    Thanks for your help, all.

  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    9,522
    Quote Originally Posted by aelectricalman View Post
    I have a customer that has come to me and said they are having major transformer overload due to harmonic distortion. We are seeing about 11% Vthd. They have some equipment where they have drilled through the concrete floor and drove a separate ground for the new peice of equipment. They have grounding issue and are tripping and burning up drives like NASCAR tires. This is a large primary user.

    There are many ways to skin this cat. I understand a power quality study should be the first approach in providing a direction. Once this is done, what type of grounding studies are out there that we could have performed to help determine if there are ground loops, high Vthd, high Ithd. I am looking at some line reactors as well but i don't want to get the cart in front of the horse.

    Thanks for your help, all.
    There should be an EGC for the equipment, and the ground electrode should not be bonded to the EGC.
    If the drives are not presenting a high power factor (distortion PF) then there will be a high harmonic content and potentially a high neutral content if it is a wye connection. Line reactors should help this, but there may be better ways.

  3. #3
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    19,428
    Quote Originally Posted by GoldDigger View Post
    There should be an EGC for the equipment, and the ground electrode should not be bonded to the EGC.
    ...
    How would you install a grounding electrode without a connection to the EGC?
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  4. #4
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    9,522
    Quote Originally Posted by don_resqcapt19 View Post
    How would you install a grounding electrode without a connection to the EGC?
    Sorry, meant to say neutral if there was one. Not EGC.

  5. #5
    Join Date
    Dec 2004
    Location
    KY
    Posts
    816
    Yeah, that was my point. Its is far from correct. They certainly have two different ground potentials. Is there a study I can have performed that will tell if there are ground loops? different potentials?
    Last edited by aelectricalman; 06-28-13 at 04:20 PM.
    Chris Hill, EE,ME,GA-CR
    Power Factor Correction

  6. #6
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    9,522
    Quote Originally Posted by aelectricalman View Post
    Yeah, that was my point. Its is far from correct. They certainly have two different ground potentials. Is there a study I can have performed that will tell if there are ground loops? different potentials?
    You can just use a long section of wire and a meter to measure any differences between the voltages at the different ground electrodes which are not connected by an EGC. You can use a series or clamp ammeter to measure the current. With a suitable probe you can connect the voltage or current waveform to a THD analyzer.

  7. #7
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    4,723
    130701-1508 EDT

    How large is the plant 5,000,000, 1,000,000, 100,000 sq-ft? 100,000 is only 316 x 316 ft. The Ford Sterling Axle plant sits on a 171 acres (about 1/4 sq-mile), and is 3,000,000 sq-ft. Their website did not tell me if distribution is ungrounded delta, but I suspect it possibly is. A million or so sq-ft Dana plant at Ft Wayne is ungrounded delta 480 within the plant. At one time this was over 1,000,000 sq-ft.

    What kind of machines in your plant? How large are individual distribution transformers? Why are ground rods being driven at machines? Are there any electric arc furnaces? Is the building a steel frame with good continuity?

    .

  8. #8
    Join Date
    May 2010
    Location
    North of the 65 parallel
    Posts
    1,477
    Quote Originally Posted by aelectricalman View Post
    Yeah, that was my point. Its is far from correct. They certainly have two different ground potentials. Is there a study I can have performed that will tell if there are ground loops? different potentials?
    What's a "ground loop"?

    ice
    Harmless flakes working together can cause an avalanche of destruction

  9. #9
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    9,522
    Quote Originally Posted by iceworm View Post
    What's a "ground loop"?
    "A groundloop occurs, when, for various reasons, the front end of your aircraft decides to switch places with the back end. We won't go into just why that happens ..."

  10. #10
    Join Date
    Aug 2009
    Location
    Tacoma, Wa
    Posts
    326
    Quote Originally Posted by GoldDigger View Post
    "A groundloop occurs, when, for various reasons, the front end of your aircraft decides to switch places with the back end. We won't go into just why that happens ..."
    oops--kinda like the student who when asked what the wind was--stuck his hand out the vent and found out it was about 100kts--right on the nose!!!
    Last edited by RichB; 07-02-13 at 06:30 AM. Reason: add text