Thread: Power and low voltage same raceway

  1. #21
    Join Date
    Apr 2009
    Posts
    155
    so can class 1 and class 2 wire be in the same raceway or not? or did that question get answered? thanks

  2. #22
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    19,215
    Quote Originally Posted by Dolfan View Post
    so can class 1 and class 2 wire be in the same raceway or not? or did that question get answered? thanks
    Conductors of class 2 or 3 circuit can not be in same raceway as a class 1 or power wiring.

    Conductors rated for power or class 1 circuits can be used for class 2 circuits and be in same raceway as other class 2 rated conductors/cables.