stallcup and holt

Status
Not open for further replies.

kimrichi

Member
in one of stallcup books he stated that ungrounded system have no neutral load [straight braker] when mike holt ststes differentley some help
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
he states that straight breaker means system is ungrounded
Is that exatly what his book says? An ungrounded 240 volt system requires the use of a straight rated breaker, but corner grounded and high leg systems also require the use of a straight rated breaker. In addition, there is no rule that says you can't use a straight rated breaker on a 120/240 volt single phase grounded system.
 

jumper

Senior Member
Is that exatly what his book says? An ungrounded 240 volt system requires the use of a straight rated breaker, but corner grounded and high leg systems also require the use of a straight rated breaker. In addition, there is no rule that says you can't use a straight rated breaker on a 120/240 volt single phase grounded system.

In addition, 240V straight rated breakers are used in 208Y/120 systems also.

Example of a common commercial breaker.

http://www.grainger.com/Grainger/GE...ribution-_-3HXR1&ci_src=14110944&ci_sku=3HXR1
 