    Quote Originally Posted by Zee View Post
    Jben,
    Very apropo that you bring up what the purpose of the WEEB is for an Enphase micro-inverter. We just figured it out, it was a mystery......
    It is to bond the racking to the inverter, not vice versa. That is to say, in order to continue the EGC and bonding of the rack - thru the rail with the WEEB, into the inverter body, which in turn is bonded with the grounding wire provided inside the AC cabling.
    In other words: you can put WEEB washers on the module clamps, a WEEB on the micro, and you are done with bonding.
    Still need the GEC. That is not bonding.
    But no WEEB splices from rail-end to rail-end horizontally; and no EGC bare copper nor WEEB-Lugs running vertically from one row to another row of rails!
    Am i off my rocker?
    Just out of curiosity, how did you solve the mystery? Did the solution come from Enphase?

  2. #12
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    655
    csoc64...what brand/model solar modules are on the job?

  3. #13
    Join Date
    Jan 2012
    Location
    CA
    Posts
    278
    Quote Originally Posted by csoc64 View Post
    Just out of curiosity, how did you solve the mystery? Did the solution come from Enphase?
    no. not from enphase.
    just the perpetual search for less work.

  4. #14
    Join Date
    Jun 2013
    Location
    northeast
    Posts
    68
    Quote Originally Posted by shortcircuit2 View Post
    csoc64...what brand/model solar modules are on the job?
    American Choice 250W modules with Enphase M215 microinverters

  5. #15
    Join Date
    Aug 2005
    Posts
    22
    The WEEB clip positively bonds the Enphase inverter metallic case to a metallic rail as part of the grounding system by penetrating any oxides or coatings on the rail or inverter case. It is quick and easy.

    Reference Enphase M215 and Engage cable: The M215 inverter has 4 wires - 2 line (red, black), 1 green equipment grounding conductor (EGC), one white grounded conductor (N). The green wire (EGC) IS NOT bonded to the metallic inverter case. The inverter also has a built-in lug.

    The Enphase Engage cable also has 4 wires of the same colors. Using standard wiring methods will bring the circuit back to the main panelboard . Of course, the green wire is not bonded to the white (N) until at the main service panel where they are bonded together.

    Since all exposed metallic parts of the PV system must be bonded together in an equi-potential plane as part of the grounding system,
    the WEEB clip easily bonds the inverter metal case to the metallic rail in a similar manner as a copper water pipe.

    With the inverter case bonded to the metallic rail, the metallic rail(s) are then bonded together using approved lugs or clips to the grounding electrode conductor (GEC) which is then bonded to the grounding electrode near the service panel.

    In lieu of a WEEB clip. a properly sized copper conductor can be bonded to each inverter case (as the GEC) using the provided lug. Each rail supporting the PV panels is also bonded to the grounding system by an approved lug holding the GEC.

    Using WEEB clips is much faster and cheaper than running long lengths of copper wire to all the components.

    As an aside, WEEB clips can also be used to bond the metallic frames of the PV panels to the grounding system instead of using copper conductor and lugs.

  6. #16
    Join Date
    May 2011
    Posts
    1,267
    Quote Originally Posted by iblittljn View Post
    ... The green wire (EGC) IS NOT bonded to the metallic inverter case. ...
    Says who?

    In lieu of a WEEB clip. a properly sized copper conductor can be bonded to each inverter case (as the GEC) using the provided lug.
    There's a pretty clear argument to be made that the GEC must be continuous or irreversibly spliced from the inverter to the grounding electrode, per the code. (That is based on the article 100 definition of a GEC, 690.47, and 250.64.) Perhaps a connection to a grounding busbar is sufficient per 690.47(C)(3), but a WEEB is definitely not an irreversible splice.

    As a matter of opinion, I think that it's a bit over the top that we have (in effect) more stringent grounding requirements for microinverter systems operating at less than 50VDC than we do for string inverter systems at up to 600VDC. But as far as the current code, it doesn't allow a WEEB to be a GEC. With that said, I understand that the 2014 will introduce some changes in this regard.

  7. #17
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    655

    UL 467

    The WEEB is a UL 467 grounding and bonding device listed by ETL...

  8. #18
    Join Date
    Sep 2004
    Location
    Midwest
    Posts
    154

    A WEEB a way

    No matter what the WEEB is actually for, on our solar install crew it is required to sing this song when installing them:


    "A WEEB-a-way A WEEB-a-way A WEEB-a-way A WEEB-a-way

    On the roof, the mighty roof, the WEEB gets torqued tonight

    On the roof, the mighty roof, the WEEB gets torqued tonight"

    Now you'll have that stupid song in your head all day. Muwahahahaaa!
    Lawrence Lile, P.E.

  9. #19
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    655
    Quote Originally Posted by lile001 View Post
    No matter what the WEEB is actually for, on our solar install crew it is required to sing this song when installing them:


    "A WEEB-a-way A WEEB-a-way A WEEB-a-way A WEEB-a-way

    On the roof, the mighty roof, the WEEB gets torqued tonight

    On the roof, the mighty roof, the WEEB gets torqued tonight"

    Now you'll have that stupid song in your head all day. Muwahahahaaa!
    Nobody torques their WEEBS. They use impact guns.