Results 1 to 3 of 3

Thread: MV Equipment Grounding Conductors

  1. #1
    Join Date
    Mar 2007
    Location
    MidWest
    Posts
    718

    MV Equipment Grounding Conductors

    Is an equipment ground in a MV 13.8kV sized any different than in LV systems, do you refer to 250.122? Looking thru. 250.180 it discusses grounded conductors and in 250.184(B)(8) indicates that it shall not carry continuous load , may be bare or insulated, shall have sufficient ampacity for fault current duty. However I do not see a reference to 250.122, why is 600V insulation on cable typically used for this? Just curious on this. Thanks..

  2. #2
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    22,859
    Take a look at 250.180.
    As far as the insulation rating, it doesn't make any difference as it is permitted to be a bare conductor.
    Don, Illinois
    “A Constitution is not meant to facilitate change. It is meant to impede change, to make it difficult to change.” – Justice Scalia

  3. #3
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    15,606
    Quote Originally Posted by don_resqcapt19 View Post
    Take a look at 250.180.
    As far as the insulation rating, it doesn't make any difference as it is permitted to be a bare conductor.
    Possibly the insulation is primarily there for mechanical and corrosion protection of the wire? And uses 600V rated insulation because that is commonly available?

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    22,859
    Quote Originally Posted by GoldDigger View Post
    ... And uses 600V rated insulation because that is commonly available?
    I would think that is the most common reason.
    Don, Illinois
    “A Constitution is not meant to facilitate change. It is meant to impede change, to make it difficult to change.” – Justice Scalia


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •