Results 1 to 3 of 3
Thread: MV Equipment Grounding Conductors
  1. #1
    Join Date
    Mar 2007
    MidWest
    Posts
    694
    Is an equipment ground in a MV 13.8kV sized any different than in LV systems, do you refer to 250.122? Looking thru. 250.180 it discusses grounded conductors and in 250.184(B)(8) indicates that it shall not carry continuous load , may be bare or insulated, shall have sufficient ampacity for fault current duty. However I do not see a reference to 250.122, why is 600V insulation on cable typically used for this? Just curious on this. Thanks..
  2. #2
    Join Date
    Feb 2003
    Illinois
    Posts
    20,126
    Take a look at 250.180.
    As far as the insulation rating, it doesn't make any difference as it is permitted to be a bare conductor.
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin
  3. #3
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    10,695
    Quote Originally Posted by don_resqcapt19 View Post
    Possibly the insulation is primarily there for mechanical and corrosion protection of the wire? And uses 600V rated insulation because that is commonly available?
  4. #4
    Join Date
    Feb 2003
    Illinois
    Posts
    20,126
    Quote Originally Posted by GoldDigger View Post
    ... And uses 600V rated insulation because that is commonly available?
    I would think that is the most common reason.
    Don, Illinois