Are you talking a passenger elevator like found in commercial or institutuional buildings?

Around my parts a sump in an elevator pit is common, but we are usually talking grain elevators - usually a class 2 hazardous location because of the grain dust.
 

Hendrix

Senior Member
Location
New England
Are you talking a passenger elevator like found in commercial or institutuional buildings?

Around my parts a sump in an elevator pit is common, but we are usually talking grain elevators - usually a class 2 hazardous location because of the grain dust.
It's located in a grocery store, to bring product up from the cellar.
 

jumper

Senior Member
Code ref. ?

620.21(A)(1)(d)

(d) A sump pump or oil recovery pump located in the
pit shall be permitted to be cord connected. The cord
shall be a hard usage oil-resistant type, of a length not to
exceed 1.8 m (6 ft), and shall be located to be protected
from physical damage.

620.85..........A single receptacle supplying a permanently installed
sump pump shall not require ground-fault circuit-interrupter
protection.
 

Hendrix

Senior Member
Location
New England
620.21(A)(1)(d)

(d) A sump pump or oil recovery pump located in the
pit shall be permitted to be cord connected. The cord
shall be a hard usage oil-resistant type, of a length not to
exceed 1.8 m (6 ft), and shall be located to be protected
from physical damage.

620.85..........A single receptacle supplying a permanently installed
sump pump shall not require ground-fault circuit-interrupter
protection.

There it is :happyyes: thanks
 