Thread: breaker tolerance

  1. #11
    Join Date
    May 2003
    Location
    Leesburg, VA
    Posts
    6,919
    Circuit breakers are tested per NEMA, ANSI, NETA and the particular manufactures specifications

    Breakers are high current tested for long time and instantaneous pick up
    Meggered-Insulation resistance test.
    Ductored/micro ohmed, DLRO (contact resistance measurement.
    Brian John
    Leesburg, VA

  2. #12
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    3,182
    Quote Originally Posted by brian john View Post
    Circuit breakers are tested per NEMA, ANSI, NETA and the particular manufactures specifications

    Breakers are high current tested for long time and instantaneous pick up
    Meggered-Insulation resistance test.
    Ductored/micro ohmed, DLRO (contact resistance measurement.
    Interesting I understand that NETA just uses NEMA/ANSI standards.
    Testing breakers is not that easy if you use factory testing techniques. Their equipment cost tens of thousands of dollars. I have the opportunity to test breakers at an actual factory test bench use to test breakers returned under warranty. I find it interesting that this type of equipment can be affordable in the field. NEMA AB4 was the only field testing method that I would accept as a valid field test.
    NEMA AB4 is the "Guidelines For Inspection And Preventive Maintenance Of Molded Case Circuit Breakers Used In Commercial And Industrial Applications."
    This publication illustrates the test setup.
    The only includes a time current trip test is at 300% of rated continuous current of the circuit breaker trip times are as included per table 5-3.
    5.6.4.1:For instantaneous a runup and pulse methods can be used. When using the run up method if done incorrectly it can destroy a breaker. As such testing one pole at a time and limiting the run up time between 2-5 sec useing an ammeter.
    5.6.4.2:The pulse method uses an oscilloscope where the pulse is 5-10 cycles.
    5.7 Covers the hold in test which is a test to varify that the breaker is capable of carrying its rated current.
    And last, contact resistance test is irrelevent. Such a test may be used as a way to compare the resistance of the contacts. The are no go or no go values as some would like.
    5.4.1 States:The millivolt drop of a circuit breaker pole can vary significantly due to inherent variability in the extremely low resistance of the electrical contacts and connectors. Such variations do not necessarily predict unacceptable performance and SHALL NOT BE USED AS THE SOLE CRITERIA FOR DETERMINAION OF ACCEPTABLILIY.
    That's straight from the "NEMA AB4" publication.
    I worked as an breaker application engineer for a major manufacturer and have been often amused by the so called field verification test.

  3. #13
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    3,353
    Quote Originally Posted by templdl View Post
    Was it a bolted fault or a mere brief contact? Remember that a breaker only has the ability to respond to current and the time that current is present within its TC trip curve.
    Yep. The instantaneous magnetic trip would be what should have worked here. Most likely, as was said, the circuit impedance limited the instantaneous fault current to a level below the mag trips on that breaker. I think (strictly from memory) that CH breakers have mag trips set at a range between 11-17X the breaker rating. So on a 20A breaker, the current would have had to jump to over 220A before the breaker would trip instantaneously.
    __________________________________________________ ____________________________
    "Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
    — Kilgore Trout (via Kurt Vonnegut)

  4. #14
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    3,182
    Quote Originally Posted by Jraef View Post
    Yep. The instantaneous magnetic trip would be what should have worked here. Most likely, as was said, the circuit impedance limited the instantaneous fault current to a level below the mag trips on that breaker. I think (strictly from memory) that CH breakers have mag trips set at a range between 11-17X the breaker rating. So on a 20A breaker, the current would have had to jump to over 220A before the breaker would trip instantaneously.
    Right on. The C- H residential breakers are at least 10x no matter what the rating. They do have a low mag option available as I recall which is 5x.
    Now SqD is just the opposite where their std is 5x and the they have a high mag 10x as an option.
    But when it comes to instantaneous any way that you look at it there are so many variables from the dynamics of an arcing fault to that of a bolted fault and the effect that the impedence has on both.
    If the current doesn't rise to a magnetude the the mag element can respond to the breaker will not trip unless the current by chance is high enough and long enough in duration to trip the breaker thermally which in very unlikely. As such there is a distinct possibility the breaker is stuck between a rock and a hard place and will do nothing at all.