GEC size reduction allowed by NEC?

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
Yet, the 2008 NEC handbook exhibit 725.3 shows an oil burner motor being part of a Class 1 circuit. If these automatic doors are controlled as part of the fire system, I think the AHJ could apply 725.31.
IMO If the circuit provides the power that moves the door the circuit is not a Remote-Control or Signaling Circuit.

I can see that this may not be a remote control or signaling circuit, yet there are remote control and signaling circuits that supply a motor of equal or greater power. Just an observation - not trying to justify that it is something it isn't.
 

kwired

Electron manager
Location
NE Nebraska
A valve damper is considered a control circuit and it has a motor in it.

Connect it to a circuit where it is the only load and some would argue it is not a control circuit, just like the door operator.

I really don't know what it is if it is stand alone.
 