    how would you shed a 100 amp sub-panel feed panel from a generac transfer switch
    the load shed modules are 50 amp max I believe
    generator and service rated switch are existing
    there are existing load shed modules for the range and dryer to get the demand just under the 17kw generator output
    we are adding the sub-panel for a basement workshop that does not need to be on the gen
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,135
    Quote Originally Posted by boltneck View Post
    You could always use a small load module to drive a contactor. Since the contactor will not be a transfer switch nor on the service side of main disconnect, there should not be any odd requirements.
  3. #3
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,240
    Don't have enough details to tell you specifically how, but find a way to connect said panel ahead of the transfer switch.
  4. #4
    Join Date
    Nov 2007
    Posts
    875
    Is there a means to place a 100A disconnect next to the meter base and feed it off the load side before it enters the transfer switch?
  5. #5
    Join Date
    Feb 2003
    Portage, Indiana NEC: 2008
    Posts
    9,911
    Quote Originally Posted by nizak View Post
    I think you meant feed from the normal (utility) side.
    Unfortunately I have never seen a Generac transfer switch with lugs rated for two conductors, maybe tap slices would work?
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe