MC Cable To Service Panel

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Although the jacket may not qualify as an EGC it still is required to be grounded which means that it needs a proper connector to attach it to the panel enclosure.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
312.5(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There are numerous ways to do this in a code compliant manner, the one depicted in the photo isn't one of them. :)
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
How come you are not connecting the MC cable directly to the panel ?
 

ksmith846

Senior Member
It looks better than the first photo and it seems to be code compliant, however I would suggest using Erico Caddy CJ6 MC Cable supports to strap that MC. It is a much quicker than screwing to the inside of the studs and it keeps the cable far away from the drywallers' screw guns.
cj6.jpg
 