    7 6 NEC Voltage Drop Recommendations


  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,160
    I keep seeing comments, in the clip and elsewhere, that talk about inductive loads taking more current at a lower voltage.
    What is really happening is that constant power loads, whether they are motors or equipment power supplies or VFDs, take more current as the supplied voltage goes down.

    Those loads will not be ohmic. They may or may not be resistive in terms of their complex impedance, but some will be inductive, some capacitive and some will have a displacement power factor arbitrarily close to 1.

  3. #3
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,311
    Don't forget the voltage drop requirements in the energy code. Requirement ... not an informational note.