Backup power question...

Status
Not open for further replies.

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)

it almost seems like for all this screwing around it might be just as cost effective to buy a real trasnfer switch.
I've not ever seen a 1600A (or 3000A) transfer switch. I'm sure someone makes one - although I don't know why. All the installations I have seen are two electric interlocked 1600A CBs in switchgear. Of course that means the install is three wire and one has to do something with the neutral - also probably still true for the proposed install.

In this case, the certification is the point. Considering the temporary gen will be used once/decade to never, the install can be pretty inconvient and it won't matter. Just needs to be safe and have a good procedure. Ful has it really, really, really, well covered. Like the man said, "I think that is enough dynamite, Butch."

ice
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor

I've not ever seen a 1600A (or 3000A) transfer switch. I'm sure someone makes one - although I don't know why. All the installations I have seen are two electric interlocked 1600A CBs in switchgear. Of course that means the install is three wire and one has to do something with the neutral - also probably still true for the proposed install.

ice

They use motorized breakers tied to a common buss, I have installed lots of 2000 amp ones. They are electrically and mechanically interlocked.
 