SETTING OFF TWO DETECTOR TO INITIATE NOTIFICATION

Status
Not open for further replies.

62Ipala

New member
Location
abilene, texas
I HAD A QUESTION ON HAVING 2 SMOKE DETECTORS TO SET OFF NOTIFICATION DEVICES. WHAT IS THE RULE ON HAVING TO SET OFF 2 DETECTORS BEFORE THE ALARMS SOUNDS??? THANKS
 

ron

Senior Member
Most jurisdictions want notification devices to begin evacuation on the first detector. Some allow you to wait for a second (cross zone) to do other actions such as release a suppression agent, etc.

Many addressable smoke detectors can also wait to activate alarm after a short period of "verification" that the smoke is still there.
 

dhalleron

Senior Member
Location
Louisville, KY
That is normally only used for suppression systems so as to be sure of a fire before dumping water or chemical on computers and such.

I have done it in production areas. An example was a building that made the crystal wafers that computer chips are made out of. They want to make very sure there is a fire before they shut down production and evacuate a building. It was allowed by the AHJ in that case.

Also, when you cross zone detectors you need to cut the normal spacing in half and be sure to have at least 2 detectors in every area.
 