I suspect that there are some. It may be a special order so check with your supplier. I bet stainless steel units are 2 hr rated but they would costs lots of mulah
 

north star

Senior Member
Location
inside Area 51
= + =

johnklinges1,

1st, ...Welcome to The Mike Holt Forum! :cool:

2nd, ..Allied Moulded Products, Inc. used to carry a complete line of
fire rated fiberglass boxes, in various sizes & ratings.....See the link:
http://www.alliedmoulded.com/index....egory/template/products_sub_ind/categoryid/89

3rd,
...as a matter of courtesy / civility / mutual reaspect, ...please
refrain from typing your questions & responses in an "All Capitilized"
manner.....This is considered to be shouting at the Forum readers. :happysad:
Thank You !

# * #
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
You don't "have" to use firepads with any rated box. Therer are a lot of inspectors that mistakingly require it, thinking that the holes in the back of the boxes are a problem. Most plastic boxes and all steel boxes are 2 hour rated. There are some situations where you might have to or can use a fire pad on your boxes and they are listed in the building code.

And as north star mentioned, Allied makes some boxes that you don't have to use the fire pads with.
 