What needs to be GFCI protected in a residential bathroom?

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
Sometimes I see the light over the tub protected, and other equipment, but not always. Thank you for your help.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would add exhaust fans over the tub, there usually required by the fan manufacturer to be GFCI protected although it's not directly required by the NEC.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
120v Receptacles are all that the nec requires except for specific equip. like a hydromassage tub. Fans over the shower and very few recessed lights over shower are required by manufacturers instructions.
 