Results 1 to 4 of 4

Thread: Generator Conductor Ampacity [445.13] Edited

  1. #1
    Join Date
    Oct 2007
    Posts
    1,282

    Generator Conductor Ampacity [445.13] Edited


  2. #2
    Join Date
    May 2009
    Location
    Usa
    Posts
    1,617
    Quote Originally Posted by Mike Holt View Post
    Thanks. Very informative.

  3. #3
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    936
    informative and made it simple...name plate of generator, get amps... multiply by 115 percent.. for size wire between generator and overcurrent device. Then wire from overcurrent device to breaker panel is sized at overcurrent device. But, this example is overcurrent device also sized at 115 percent basically... so, all sections covered...
    however, what if all you have is three thousand watt generator with surge up to five thousand watts, rated for 120 or 240volts? Just convert to volts based on surge wattage? Or on normal wattage?

    And would inverters be sized the same from battery banks?

  4. #4
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,588
    The video may go on after the free version stops, but the exception for 445.13 applies to many of the large custom generators that have internal protection from overloads, which would limit the sizing to 100% of nameplate.
    Ron

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •