User Tag List
Page 1 of 3 1 2 3 LastLast
Results 1 to 10 of 29
Thread: Compact conductors
  1. #1
    Join Date
    Jun 2013
    loveland colorado
    Posts
    81
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Compact conductors
    Correct me if I'm wrong. Most all of wire made these days is considered a compact conductor? Does it list it on the insulation? Ive never seen it. I was told 90% of wire is made to be a compact conductor.
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,032
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by olly View Post
    All of the aluminum wire I get is of the compact type.
    None of the copper wire I get is compact.
    You can tell compact conductors by the shape of the strands, if the individual strands are not round you have a compact conductor.
  3. #3
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Who told you that?
    I thought most conductors were actually just regular stranded and compact conductors would have to be specifically ordered/asked for.
    I am pretty sure I have never used them. I have never ordered them nor have seen them speced on my jobs.
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #4
    Join Date
    Jan 2009
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by iwire View Post
    Oops. Once again, I stand corrected. Thanks Bob, I had not known that.
    Derek
  5. #5
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,878
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Same here out west.
    If you don't think too good, don't think too much.
  6. #6
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,943
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    In my experience most general purpose wire (excluding service conductors and MV/HV) is neither compact nor even compressed.
    I think you will also be more likely to find compact construction in Al wire, since it is softer.
    Compact construction makes stranded wire more difficult to bend for the same metal cross section and stranding.
    I doubt that compact will be specified on the wire itself; you would have to look at the product specifications.
    That said, for service, transmission, and distribution lines compact stranding does seem to be popular. For overhead lines it reduces the wind resistance cross section for the same amount of metal and for cables and insulated wires it also reduces the voltage stress on the insulation surrounding the wire.
  7. #7
    Join Date
    Jan 2009
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    Same here out west.
    Do you have to ask for it or is it just standard?
    Derek
  8. #8
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,179
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    IN an earlier post fmtjfw pointed out the following:
    UL White Book 2013 ZKST Thermoset-Insulated Wire and ZLGR Thermoplastic-Insulated Wire:
    Wire and cable employing compact-stranded copper conductors is so identified directly following the conductor size, wherever it appears (surface, tag, carton or reel), by ‘‘compact copper.’’ The abbreviations ‘‘CMPCT’’ and ‘‘CU’’ may be used for compact and copper, respectively.
    Tags, reels and cartons for product employing compact-stranded copper conductors have the marking: ‘‘Terminate with connectors identified for use with compact-stranded copper conductors.’’
    AL wires are also in the same sections.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  9. #9
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,032
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    My understanding is the entire point of making AL compact is so AL conductors of the same ampacity as copper conductors will fit in the same conduit.
  10. #10
    Join Date
    Jan 2009
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Well, what do you know, I've been installing compact AL and never paid attention.
    I went to Southwire's site and as Bob said it is compact AL. AA-8000.
    Damn, I know I never figured compact wire for conduit sizing. Ooops.
    Derek
Posting Permissions