Can type CL-2 thermostat wire enter an enclosure with 240 volt circuits?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Can type CL-2 thermostat wire enter an enclosure with 240 volt circuits?
1. It can if there is a partition between the two voltages.
2. If the enclosure and the controls within it are part of a listed product, then you have to follow the instructions. If it is all field wiring, see 1. above.
 

Galt

Senior Member
Location
Wis.
Occupation
master electrician and refrigeration service tech.
How about RIB type relay with 24 volt control all the wires come out of the same nipple. Also just about every contactor I have seen would be very difficult to isolate the two?
 

nhfire77

Senior Member
Location
NH
IIRC, When there is only one opening they can be mixed for a piece of listed equipment. there is an exception in 725 for that, but it's limited. (no pun intented)
 