Grounded why delta is a very poor choice because any fault on the feeder will blow those fuses regardless of the arrestors because a wye grounded-delta transformers are nothing but a giant grounding transformer. They are the ultimate zero sequence source and will "absorb" any neutral/ground current. They are used where a neutral is needed like on a ungrounded delta system, and in fact where grounded wye primary - delta secondary transformers are applied to substations (115-34.5kv) engineers actually have to consider an increase in fault current at the primary 115kv station bus and adjust protective relaying/arc flash studies to take this into account.
As for ferrorrsonance, it can happen on some ultra high efficiency (amorphous metal) wye grounded primary transformers from what I have read. Another thing that pops into my mind are capacitor banks. Over compensated lines and those where a cap bank has blown a fuse but the other two phases remain compensated can cause over voltage, and I've heard heard of line resonant conditions also occurring under those circumstances. Its possible (theory) that when loaded the caps are doing their job, voltage within spec, ect and when the load is shed the line is over compensated (improper settings or fixed bank). When closed unloaded the over compensated line resonates with the transformer's inductance causing an over voltage and in turn the arrestors to flash over blowing fuses. Its a guess, but it is a plausible theory imo.
I know I keep subverting the conversation away from those arrestors but fuses and a wye delta are two immediate red flags for me, because its likely those fuses will continue to blow every time a fault occurs on the feeder (or even other feeders) even if the lightning arrestor condition is solved.
But, that does not mean you should stop probing further. My gut right now is to talk to the POCO about cap banks and how that line is compensated under load. Good time to ask about voltage regulators (those need to have their line drop impedance settings set correctly in order to provide the right voltages) Id also have the POCO verify all the banks have fully functional fuses and see if they can obtain voltage, reactanace, ect conditions with your line unloaded. My gut (and its just an educated guess) that there is some type of over voltage condition causing those arrestors to flash over.




Bookmarks