Page 3 of 4 FirstFirst 1234 LastLast
Results 21 to 30 of 31
Thread: 250.122(F)
  1. #21
    Join Date
    Apr 2016
    Georgia
    Posts
    454
    Quote Originally Posted by GoldDigger View Post
    An EGC run separately from the line may, for example, decrease the current from a bolted fault from 25kA to 10kA, but is not likely to affect the trip time of OCPD.
    You probably enjoy sky-diving and swimming with sharks... Just guessing here. Point is, why take the chance?
  2. #22
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by Dale001289 View Post
    The real point is, why add a code restriction with no real world evidence there is a safety issue?
    So far all you have done is presumed there is a safety issue based on an exsiting rule for a similar installation.
  3. #23
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,172
    I considered closing this thread since you have ignored the rules (you read them but didn't pay attention to them) for this particular forum. However, since at least four other moderators have commented, I'll let it slide this time. In the future, if you ignore them again, I'll delete the thread as spam.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.
  4. #24
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,524
    Quote Originally Posted by rbalex View Post
    Speaking for myself, I did not notice that the thread was in the Proposals forum. I bet some of the others made the same mistake.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  5. #25
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,195
    Quote Originally Posted by ActionDave View Post
    Ditto.
    "Electricity is really just organized lightning." George Carlin
    Derek
  6. #26
    Join Date
    Feb 2003
    Fl
    Posts
    17,134
    Quote Originally Posted by jumper View Post
    Ditto.
    Guilty too
    Roger
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,775
    . . . the rules . . .
    Thanks for the link to the Rules. That was a good read. I hadn't realized the "special handling" engendered by this Forum section.
    Good to know.
    Another Al in Minnesota
  8. #28
    Join Date
    Feb 2003
    Illinois
    Posts
    23,581
    I just looked a trip curve for a 100 amp breaker. A 25,000 amp fault is clearly in the instantaneous trip part of the band, but the trip time for a 10,000 amp fault could be anywhere from instantaneous to 2 seconds.
    Edit....those numbers are off by a factor of 10. The currents should be 1000 and 2500 amps, so there would be no difference with that breaker between a fault current of 10,000 and 25,000 amps.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  9. #29
    Join Date
    Apr 2016
    Georgia
    Posts
    454
    Quote Originally Posted by don_resqcapt19 View Post
    don, nice research. I'll bet those 2 seconds will increase as the distance increases, i.e. EGC relative to circuit conductors.
  10. #30
    Join Date
    Feb 2003
    Illinois
    Posts
    23,581
    I will make that mistake every time....I never look at what forum a thread is in....I just look at new posts.
    Don, Illinois
Posting Permissions
  • You may not post replies
  • You may not edit your posts