User Tag List
Page 2 of 3 FirstFirst 1 2 3 LastLast
Results 11 to 20 of 24
Thread: 210.12(B) Exception: AFCI 6ft rule
  1. #11
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,364
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I can't imagine why the inspector is using the conductor length both ways.... Assuming nm cable then how would 3' of nm being of any help at all... the inspector is in error.
    Ask the inspector how he would calculate a multiwire branch circuit--- 2' of cable???? Makes no sense
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  2. #12
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,153
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    Make it a three phase MWBC and you only get 18".
    Extend two of them as part of the same panel move and get 9"?
  3. #13
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,364
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    Yep, gets absurd doesn't it. Not sure if the inspector is just being difficult or if he really thought it was meant to be that way. I can assure him he is ioncorrect
  4. #14
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,032
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    IMO, the 6' distance can be very tight in many instances even between enclosures.
    No doubt, even the 10' tap rule can be tough to comply with.
  5. #15
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,001
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yep, gets absurd doesn't it. Not sure if the inspector is just being difficult or if he really thought it was meant to be that way. I can assure him he is incorrect
    I agree and really would 3' or 6' make any difference? Your proposal was great because it adds direct language as to how the distance is measured and takes care of an extremely common installation.
    Rob
  6. #16
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    8,098
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    In Washington we had a state rule that limited the length of unfused service entrance conductors in a building to 15 feet of conductor. This proved to be difficult to measure, so it was changed to 15 ft of raceway.
    Moderator-Washington State
    Ancora Imparo
  7. #17
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    2,027
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I was a bit concerned that the panel was required to be moved from a landing area -- if there is compliant clear space on a landing is it really a step?
    I do find it a bit disturbing that an inspector is required to measure the make up inside a panel & device box -- you would be eliminating 2-3' on every installation, I use the KISS rule as most measurements are from edge of water/basin/storage space/front of panel/ which would be consistent with jbox to jbox -- show me where the major difference in 9' to 6' as an extension is a life safety factor . There is an option to run up to 70' of 12-2nm without any protection to first device so why would a few extra feet be so critical???
    KISS
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.
  8. #18
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,191
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tom baker View Post
    Now you have people that think there is no limits on cable methods right?
  9. #19
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,364
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mwm1752 View Post
    KISS
    That is only when using a breaker and device that are listed together. There is no such device afaik.. Anyway I agree 6' is too short even without counting the wire inside the enclosure
  10. #20
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    2,027
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Brain fart Dennis thanks for keeping me in line
Tags for this Thread
Posting Permissions
  • You may not post replies
  • You may not edit your posts