Results 1 to 10 of 10
Thread: Dual Circuit Lighting Track and NEC article 700
  1. #1
    Join Date
    Dec 2008
    Towson, MD
    Posts
    40
    I have a project where it has been proposed to use dual circuit lighting track with one circuit used for normal power lights and the other circuit used for emergency lights. Someone reviewing the project electrical drawings said this would violate NEC 700.10(B).
    NEC 700.10(B)(2) says "Wiring supplied from two sources in exit or emergency luminaires" is permitted, so you can have both normal and emergency wiring entering a luminaire.
    NEC 100 defines luminaire as "a complete lighting unit consisting of a light source such as a lamp or lamps, together with the parts designed to position the light source and connect it to the power supply. It may also include parts to protect the light source or the ballast or to distribute the light. A lampholder itself is not a luminaire."
    Based on the definition of a luminaire, the track and the track heads together make up a luminaire. This is obvious but the reviewer doesn't buy it. He wants to know if the track and heads are UL listed for emergency operation, which doesn't make sense because, as far as I know, UL924 and 1008 don't apply to luminaires but to bypass and transfer equipment.
    My questions are:
    1. Are track and track heads ever UL listed for emergency operation?
    2. Are there any NEC based arguments for track and track heads as a system to not be considered a luminaire?
    Please provide answers/arguments based on the NEC or UL standards. I have been through too many discussions based on speculation.
    Thanks.
    F413
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Any two, or three circuit track I have ever worked with uses a common neutral conductor therefore you cannot supply it from different panels at the same time.
    In my opinion that ends the idea right there.
  3. #3
    Join Date
    Dec 2008
    Towson, MD
    Posts
    40
    Quote Originally Posted by iwire View Post
    The track my lighting designer is specifying will have dedicated neutrals.
    F413
  4. #4
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by patrox2000 View Post
    Interesting. Do you have a part number for it?
    I cannot help you with your questions do I will step aside.
  5. #5
    Join Date
    Dec 2008
    Towson, MD
    Posts
    40
    Check out the "DataTrack" by ETC. Separate neutrals is listed under the features sections of the data sheet.
    https://www.etcconnect.com/Products/Distribution/DataTrack/Documentation.aspx
    F413
  6. #6
    Join Date
    Dec 2010
    Posts
    1,381
    You probably need equipment that is UL listed as FTBR
    http://database.ul.com/cgi-bin/XYV/t...830&sequence=1
    And 924 covers luminaires
    http://ulstandards.ul.com/standard/?id=924
  7. #7
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Thanks.
  8. #8
    Join Date
    Dec 2010
    Posts
    1,381
  9. #9
    Join Date
    Feb 2003
    Pennsylvania
    Posts
    2,365
    My questions are:
    Thanks.
    My thought would be if the fixture has a thermal overload than the fixture would not be suitable for egress emergency lighting as you described the application.
    I further doubt UL would list any fixture with thermal over load protection as suitable for emergency lighting
    look at 410.130 (E) (4) 2008
    "Section 410.130(E)(4) exempts egress lighting from the thermal protection requirement for the same reason that exit signs are exempt. However, this exemption applies to egress lighting that is energized only during the emergency condition"
    NFPA Handbook comment
  10. #10
    Join Date
    Mar 2017
    New York NY
    Posts
    2
    My questions are:
    Thanks.
    If the track-mounted luminaires contain a control input, they become Directly Controlled Luminaires per NEC 700.2 and 700.24. This requires them to be Listed for emergency under UL924.
    Specific wording on Directly Controlled Luminaires was added to the 10th edition of UL924 on March 9, 2017. Therefore, it is reasonable to expect that manufacturers will now start obtaining a UL924 listings on Directly Controlled Luminaires.
    As to the question of the 2-circuit track and separation of circuits, there is no specific allowance in 700.10(B) for such an arrangement. Therefore, it could be argued that the current NEC does not allow such an arrangement. However, I think a discussion with the applicable AHJ would be the best course of action. In addition, who knows what proposals might be made in the 2020 Code Cycle, even by yourself?