240.6

Status
Not open for further replies.

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
I keep a copy of the page that has 240.6 Standard Ampere Ratings taped to the wall in my cube. Something that has always made me wonder is the additional standard rating of 601A. Why is that? Is there really any difference between a 600A fuse and a 601A fuse?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
There are no fuse reducers for Class L fuses, so a 601A fuse in an 800A switch would be kind of like putting 60A fuses in a 100A switch.
 
Status
Not open for further replies.