Page 1 of 3 123 LastLast
Results 1 to 10 of 21
Thread: Insulated Throat EMT Connectors and 300.4(G)
  1. #1
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,383
    Having a discussion recently as to whether or not an EMT connector with an insulated throat meets the intent of 300.4(G) (when used with conductors #4 and larger) in lieu of a plastic bushing. My opinion is that they are complaint because they meet the requirement of the last sentence because they are fastened in place.
    300.4(G) Insulated Fittings. Where raceways contain 4 AWG or larger insulated circuit conductors, and these conductors enter a cabinet, a box, an enclosure, or a raceway, the conductors shall be protected by an identified fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by identified insulating material that is securely fastened in place.
    Rob
  2. #2
    Join Date
    Jan 2007
    Posts
    3,234
    Quote Originally Posted by infinity View Post
    If I didn't know what a plastic bushing was, I'd say you just described the fitting in the picture.
    JAP>
  3. #3
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    If I were an inspector, I'd let the fitting you pictured slide... but on a personal level I don't think they should be permitted to be compliant. I say this because there is no rounded throat on that fitting, and deeper into the fitting, the fitting metal is not separated from the conductors by the insulating throat.
    Compare to rounding of this throat...
    I will have achieved my life's goal if I die with a smile on my face.
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,383
    I would guess that the fitting in post #1 would keep the conductors from touching the actual fitting. The rounded insulating surface refers to an external bushing so I would see either of those pictured as being compliant.
    Rob
  5. #5
    Join Date
    Jul 2003
    MA
    Posts
    2,040
    The fitting insulation is rounded in post #1.
    It just has a smaller radius that the fitting in post #2.
    There is no requirement for the rounded radius.
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices
  6. #6
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by tkb View Post
    I think the rounding should at least be discernible by the naked eye...
  7. #7
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    18,795
    Quote Originally Posted by Smart $ View Post
    There is a very discernible rounding in the red plastic of the connector shown. Unfortunately that radiused part is on the outside of the indiscernibly rounded inner edge.
  8. #8
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by GoldDigger View Post
    By golly you are correct.
    The section text is of no help. I inferred the rounded surface is to be the one the conductors make contact with.
  9. #9
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,156
    Compliant IMO also.
    "Electricity is really just organized lightning." George Carlin
    Derek
  10. #10
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,383
    I've used these without an external plastic bushing on some larger EMT runs and found that the internal insulated throat didn't survive the rope and nose of the cable coming through it. Typically they popped right out and if you were lucky they didn't break and could be reinstalled.
    Rob
Posting Permissions
  • You may not post replies
  • You may not edit your posts