Page 1 of 2 12 LastLast
Results 1 to 10 of 13
Thread: AL vs CU cost analysis
  1. #1
    Join Date
    Sep 2012
    NJ
    Posts
    2,029
    Anyone ever do an analysis of the % diff between the two material and labor when substituting for a particular amperage....obviously have to upsize for AL?
  2. #2
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,516
    I did and it was cheaper to use AL over CU above 200A.
    Ron
  3. #3
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,381
    Quote Originally Posted by mstrlucky74 View Post
    I don't see any significant Increased labor in going up a pipe size. Copper is heavier than aluminum so that is a factor for pulling
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  4. #4
    Join Date
    Sep 2012
    NJ
    Posts
    2,029
    Sorry should've been more clear. Scenario I'm referring to is when you have EMT and thhn copper conductors and want to switch to aluminum conductors. I often see a lot of value engineering requests for this.
  5. #5
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,335
    I think that much of the potential savings depends on how high your labor rate is. Factoring in more or larger conduits, larger or more sets of conductors on parallel runs and more terminations can diminish your savings if you have very expensive labor rates.
    Rob
  6. #6
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
  7. #7
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,785
    Something I have noticed is that parallel 1/ 0 is about the cheapest ampacity you can get with the side benefit of being easier to work with as opposed to using a single larger cable.
    Bob
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,056
    The application conditions do have some impact.
    If you were making a 1000 foot run underground in PVC - the need to increase the raceway a size probably doesn't impact labor as much as needing to increase GRC a size that is being installed 30'+ high in a high bay building, especially once you start to go beyond 2 inch trade size.
  9. #9
    Join Date
    Sep 2012
    NJ
    Posts
    2,029
    Quote Originally Posted by infinity View Post
    Good point.
  10. #10
    Join Date
    Jul 2017
    Bristol
    Posts
    2
    Interesting. I've recently switched to CU myself.
Posting Permissions
  • You may not post replies
  • You may not edit your posts