    I'm thinking of proposing a change to 705.12(B)(2)(b), and I'm hoping for some input.
    It seems to me that the current rule makes complete sense for basic panelboards
    that have a main breaker and a bunch of identical branch breaker provisions on the
    load side of the main breaker. It doesn't seem to anticipate panelboards that have
    provisions for a sub-feed breaker and where the secondary power source is
    connected using a branch breaker instead of a sub-feed breaker.
    The current language is:
    Where two sources, one a primary power source and the other another
    power source, are located at opposite ends of a busbar that contains
    loads, the sum of 125 percent of the power source(s) output circuit
    current and the rating of the overcurrent device protecting the busbar
    shall not exceed 120% the ampacity of the busbar. The busbar shall be
    sized for the loads connected in accordance with Article 220. A
    permanent warning label shall be applied to the distribution equipment
    adjacent to the backfed breaker from the power source that displays the
    following or equivalent wording:
    WARNING:
    POWER SOURCE OUTPUT CONNECTION,
    DO NOT RELOCATE THIS OVERCURRENT DEVICE
    The warning sign(s) or label(s) shall comply with 110.21(B).
    Exception: Equipment with multiple ampacity busbars or center fed
    panelboards are not addressed by this provision.
    I propose to change this to:
    power source, are located on a busbar that contains loads and the
    primary power source is at one end of the busbar, the sum of 125 percent
    of the power source(s) output circuit current and the rating of the
    overcurrent device protecting the busbar shall not exceed 120% the
    ampacity of the busbar. The busbar shall be sized for the loads
    If the backfed breaker from the power source is at the opposite end of
    the busbar from the primary power source and no devices or taps can be
    installed beyond it, then a permanent warning label
    shall be applied to the distribution equipment adjacent to the backfed
    breaker from the power source that displays the following or equivalent
    wording:
    WARNING:
    If the distribution equipment allows additional devices or taps to be
    installed between the backfed breaker from the power source and the end
    of the busbar opposite the primary power source, then all of the
    following are required:
    (i) No taps may be made between the backfed breaker from the power
    source and the end of the busbar opposite the primary power source.
    (ii) The sum of the ratings of any overcurrent devices between the
    backfed breaker from the power source and the end of the busbar opposite
    the primary power source must not exceed the rating of the busbar.
    (iii) A permanent warning label shall be applied to the distribution
    equipment adjacent to the backfed breaker from the power source that
    displays the following or equivalent wording:
    WARNING:
    DO NOT RELOCATE THIS OVERCURRENT DEVICE.
    NO TAPS MAY BE MADE ON THE BUS BEYOND THIS OVERCURRENT DEVICE,
    AND THE SUM OF THE RATINGS OF ALL OVERCURRENT DEVICES
    BEYOND THIS DEVICE MUST NOT EXCEED THE RATING OF THE BUS.
    Substantiation: I think the current language is somewhat dangerous and
    unnecessarily restrictive.
    Imagine a 200A top-fed main breaker panel that has an unused provision
    for a sub-feed breaker at the bottom. Under the current language, it is
    probably acceptable to install a 40A breaker (for a 32A power source) at
    the bottom of the panel just above the sub-feed provision as long as
    it's labeled with a warning sign saying "WARNING: ... DO NOT RELOCATE
    THIS OVERCURRENT DEVICE". The installation would be safe as is.
    However, a future electrician could see that sign, and, without thinking
    about it hard enough, install a 200A subfeed breker at the bottom. The
    result would still be safe (no part of the busbar could be overloaded),
    but it would no longer comply. If sub-feed lugs were to be installed,
    the result would be unsafe: the bus between the lugs and the 40A breaker
    could be overloaded.
    On the other hand, there are simple installations that would be safe but
    are not permitted. Imagine the same 200A panelboard with a 40A breaker
    for the secondary power supply at the lowest normal breaker position
    and a 200A sub-feed breaker at the very botton. This would be entirely safe:
    the bus between the 40A breaker and the sub-feed breaker would be protected by
    the sub-feed breaker and the bus above the 40A breaker would be protected
    as it would be if the breakers were in the other order.
  2. #2
    Join Date
    Oct 2016
    Posts
    7
    The language I wrote was a bit messy. This version may be better.
    the busbar from the primary power source and no devices or conductors
    can be installed on the busbar beyond it, then a permanent warning
    label shall be applied to the distribution equipment adjacent to the
    backfed breaker from the power source that displays the following or
    equivalent wording:
    WARNING:
    If the distribution equipment allows additional loads to be connected
    between the backfed breaker from the power source and the end of the
    busbar opposite the primary power source, then the following conditions
    must be met:
    (1) The backfed breaker must be installed as far as practicable from
    (2) The sum of the ratings of the overcurrent devices protecting loads
    connected between the backfed breaker from the power source and the
    end of the busbar opposite the primary power source must not exceed
    (3) A permanent warning label shall be applied to the distribution
    WARNING: POWER SOURCE OUTPUT CONNECTION, DO NOT RELOCATE THIS
    OVERCURRENT DEVICE. THE SUM OF THE RATINGS OF OVERCURRENT DEVICES
    CONNECTED BEYOND THIS DEVICE MUST NOT EXCEED THE RATING OF THE BUS.
  3. #3
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    The 2017 NEC does not have that Exception according to the online version.
    While I understand your concern, it mostly involves an installation to being taken out of compliance after original installation. I say a slight change to the sign wording would be sufficient...
    WARNING: POWER SOURCE OUTPUT CONNECTION.
    2020 NEC §705.12(b)(2)(b) COMPLIANT. DO NOT RELOCATE
    OR ADD LOADS WITHOUT VERIFYING NEC COMPLIANCE.
    I will have achieved my life's goal if I die with a smile on my face.
  4. #4
    Join Date
    Oct 2016
    Posts
    7
    Quote Originally Posted by Smart $ View Post
    Whoops, I need to fix that.
    That would address the safety concern but not the usefulness concern.
    Panels with sub-feed breakers are unusual in residential applications but aren't particularly rare, and allowing such a panel to have a utility-interactive inverter attached at the farthest normal breaker position next to the sub-feed breaker seems both safe and useful. My main intent would be to explicitly allow such an installation under the 120% rule.
    This could be done with a narrower change along the lines of "Exception: If the backfed breaker is connected to the busbar as possible from the primary source, then a single sub-feed breaker may be installed beyond it so long as the sub-feed breaker's rating does not exceed the busbar's rating." It seems worthwhile to make the exception more general, though.
  5. #5
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by amluto View Post
    Doesn't an end-of-bus sub-feed breaker (or feedthrough) contradict the opposite end condition. The backfed breaker is technically NOT at the opposite end as there would be loads being fed both above and below.
  6. #6
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,244
    That is why the subfeed breaker must be rated at or below the bus rating.
    The problem in general is that if you allow multiple breakers beyond the backfed breaker they can add up to more than the bus rating.
  7. #7
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by GoldDigger View Post
    And what I'm saying is if you feedthrough directly or through a sub-feed breaker, you are no longer backfeeding at the opposite end of the bus in a normal breaker position.. and thus subject to 705.12(B)(2)(3)(a) requirements* which has it covered.... and all of this is subject to change in the future and thus the outlet (or prevention) is provided in the sign verbiage.
    *I'm hoping I'll get a deal on a NEC 2017 pdf & softbound like I did last cycle. Hasn't happened yet so not able to conveniently quote the section.
  8. #8
    Join Date
    Oct 2016
    Posts
    7
    Assuming I transcribed it right from the free online version, it says:
    The sum of 125 percent of the power source(s) output circuit current and the rating of the overcurrent device protecting the busbar shall not exceed the ampacity of the busbar.
    My reason for proposing the change is that I think that this text disallows a useful and safe installation. Imagine a panel with a 400A busbar, a 400A main breaker on top, a bunch of breaker provisions, and an empty sub-feed provision at the bottom. Let's say that the power source output current is 80A and the power source is connected to a 80A breaker at the bottom-most non-sub-feed position in the panel.
    Under 705.12(B)(2)(3)(b), I expect most AHJs to accept this installation as long as the sub-feed provision is unused. It would certainly be okay if the sub-feed provision were not present because 400A + (1.25 * 64A) = 480A, which is 120% of the busbar ampacity. Let's think about why this is safe. The middle of the busbar is protected because current flowing downward is limited by the 400A main device and current flowing upward is limited by the (continuous) 64A output capacity of the power source. Assuming that there aren't terrible harmonics or excessive reactive current going from one load to another, there won't simultaneously be current flowing up the bus and down the bus, so the middle of the bus is protected. The top of the bus is protected by the 400A main device (the panel would presumably never pass UL testing if the contacts to the 400A main device could be overloaded), and the sideways bus stubs at the bottom where the 80A device is attached are protected because the panel's instructions will say something like "the sum of the ratings of devices on each pole may not exceed 100A". This is the point of 705.12(B)(2)(3)(b).
    Now suppose that someone installed a 400A sub-feed breaker. (This would be a bit silly, but the panel could plausibly allow this.) This would not be allowed under the 2017 NEC as far as I can tell. Nonetheless, I would argue that it is still safe: everything from the 80A backfed breaker up is protected for the same reason that it would be without the sub-feed breaker. The contacts to the sub-ffeed breaker are protected by the sub-feed breaker. The bus between the 80A backfed breaker and the sub-feed breaker is also protected by the sub-feed breaker. (Even if there were two sub-feed breakers, it would still be safe as long as the sum of the ratings of the sub-feed breakers did not exceed 400A.) I would like for this case to be permitted.
    The installation that should not be allowed is for feed-through lugs to be installed in the sub-feed position. With the power supply running at full output, the feed-through lugs could draw 384A continuously or 464A for a few hours without tripping any of the overcurrent devices, either of which exceeds the rating of the busbar. (If the whole installation were 100% rated, then the 464A short-term draw would still exceed the rating.)
  9. #9
    Join Date
    Dec 2012
    Posts
    19,244
    Unfortunately the whole 120% rule is a compromise between physics and CYA.
  10. #10
    Join Date
    Oct 2016
    Posts
    7
    Isn't the whole NEC more or less this compromise? That doesn't necessarily mean that a more lenient rule here couldn't still achieve the CYA goal.