250.92(A) requires a bonding jumper on the line side of a conduits entry attached with a bonding bushing. (correct me if I'm wrong).
In my picture the system there is a supply side bonding jumper that goes from the transformer into this main panel and down to the grounding bar. The other green wire goes to the bonding bushing, back through the pipe, and to the transformer. I'm not sure what the inside of the transformer looks like.
So isn't the bonding wire on the bonding bushing suppose to go just the the ground bar inside this panel?
In my picture the system there is a supply side bonding jumper that goes from the transformer into this main panel and down to the grounding bar. The other green wire goes to the bonding bushing, back through the pipe, and to the transformer. I'm not sure what the inside of the transformer looks like.
So isn't the bonding wire on the bonding bushing suppose to go just the the ground bar inside this panel?