    Gas Station

    These are pictures from a recent gas station installation for dispenser and pump control. Another electrical contractor used a mix of old and new equipment. I am meeting with the inspector next week to give input on the code violations and what can be done to fix them. My biggest question is on the seal offs..... In my opinion the are not sealing the vapor from intruding as the seal is at the bottom of the seal off and nothing would prevent fuel vapor from leaking by the threads unless they were somehow air tight. Any input?
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG_1191.jpg 
Views:	198 
Size:	139.6 KB 
ID:	16395   Click image for larger version. 

Name:	IMG_1190.jpg 
Views:	196 
Size:	145.5 KB 
ID:	16396  

  2. #2
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    4,714
    It appears that this electrical equipment and wiring is installed in a vault. If it is, my professional opinion is to run like hell.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  3. #3
    Join Date
    Jan 2017
    Location
    Upstate New York, USA
    Posts
    2
    My initial thoughts were to dig up sidewalk and route conduits to gutter and install seal offs outside. Fill hole in foundation with concrete and run conduits from new gutter, through wall, and use LBs to get back into basement where electrical equipment is. They are looking for something more budget friendly, figured I'd see if anyone had ideas.

  4. #4
    Join Date
    Jan 2008
    Posts
    147
    Seen this many times with a basement install of conduits. Should have brought conduits in level, first thread seal off, then go down to trough. I think if you filled the existing seal offs full it would seal but I doubt they are listed to be 45 degree angle. How many dispensers out front?

  5. #5
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    16,880
    Quote Originally Posted by rbalex View Post
    It appears that this electrical equipment and wiring is installed in a vault. If it is, my professional opinion is to run like hell.
    The ladder and the raceways coming in just below the top?

    How far away from the dispensers and tanks would a below-ground vault have to be to avoid classification?

  6. #6
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,080
    I would agree with the others. I would add , Where are the switched neutrals in the panel?

  7. #7
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    4,714
    Quote Originally Posted by GoldDigger View Post
    ...
    How far away from the dispensers and tanks would a below-ground vault have to be to avoid classification?
    A long, long, long way. See Section 514.8. The key words are "... the point of emergence above grade" in the second sentence.

    Historically, the Technical Committee (TC) that controls NFPA 30A (from which a good chunk of Article 514 is derived) has treated spillage at dispensers a source for Division 1 for any raceway, for any distance, that runs beneath any classified location, Division 1 or 2.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  8. #8
    Join Date
    Jan 2008
    Posts
    147
    Quote Originally Posted by rbalex View Post
    A long, long, long way. See Section 514.8. The key words are "... the point of emergence above grade" in the second sentence.

    Historically, the Technical Committee (TC) that controls NFPA 30A (from which a good chunk of Article 514 is derived) has treated spillage at dispensers a source for Division 1 for any raceway, for any distance, that runs beneath any classified location, Division 1 or 2.
    Thats very interesting. So conduits coming from a gas dispenser into a basement would make that basement an area where everything would have to be class 1?

  9. #9
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    4,714
    Quote Originally Posted by wallyworld View Post
    Thats very interesting. So conduits coming from a gas dispenser into a basement would make that basement an area where everything would have to be class 1?
    It doesn't quite say that but it is a requirement unique in the main text of Section 514 to stub up from a underground run below classified locations. Other Sections or their Exceptions with similar underground runs only say, "... to the point of emergence." See for example, Section 501.10(A)(1)(a) Exception. BTW, that Exception refers to some other examples of Sections/Exceptions of similar underground installations.

    Technically, the issue is how/where to seal an underground boundary with all the other arcane requirements of boundaries seals.

    It has been a while that I am aware of any attempts to have Section 514.8 conform with the simpler requirements of other Sections/Exceptions of the NEC. It has always been rejected since the NFPA 30A TC must also concur.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  10. #10
    Join Date
    Jan 2008
    Posts
    147
    Quote Originally Posted by Sierrasparky View Post
    I would agree with the others. I would add , Where are the switched neutrals in the panel?