    Quote Originally Posted by Chamuit View Post
    Replace them with UBI breakers. You can buy them at HD.
    They are ETL listed devices. Connecticut Electric, look at "Overview."
    Thank you for the idea!
    I believe this is the best option for a customer that is unwilling to have a panel change. At minimum I can require the double pole breakers be changed if I accept work with this type panel.
  2. #12
    Join Date
    Apr 2007
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,908
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by markebenson View Post
    everyone has their own comfort level.
    i'm comfortable replacing problematic equipment.
    otherwise, i will leave it be, and the person can get
    someone else to do what they want done. i won't
    charge for showing up, and finding out the customer
    isn't a customer after all.
    they are someone else's customer.
    yeah, you can replace breakers with home desperate
    etl approved breakers, or.... you can replace the panel,
    or.... you can walk away. three options.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~
  3. #13
    Join Date
    Mar 2016
    The Motor City, Michigan USA
    Posts
    1,027
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ... I cannot think of a reason that any functional 20 a circuit breaker would not trip when shorted directly to ground.
    Possible reasons:
    - Not enough I²T (current² & time)
    There's a difference between a bolted fault and waving a pigtail around. An arc will form, which will have a higher impedance than intimate metal-to-metal contact. A magnetic field will form, which will tend to open the "connection" between the end of the pigtail and the ground. The contact point may be contaminated with paint, rust or other debris. The connection between the white wire and the box may be marginal. (remember, current must return to its source, not necessarily to the "ground")
    - Too much current
    In the past, breakers were designed to interrupt lesser fault currents, often 5 kA. If the neighborhood distribution has been upgraded, there might be more fault current available than the breaker was ever expected to handle and the contacts might weld closed before the mechanism has a chance to act. (especially if the contact resistance is higher than expected, or the mechanism is slower than expected, due to contamination or weak spring tension)
    To be clear: I do NOT advocate repeating this experiment, let alone conducting a "better" experiment with a bolted fault.
  4. #14
    Join Date
    Feb 2006
    Remotely running business in Bay Area, CA from Medford, OR
    Posts
    1,066
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    Thanks Augie47! I will keep them for future inspections/quotes.
    Though usually I just suggest the homeowner do their own research, lest they feel I'm just trying to sell them a service change. But the nbcbayarea report was excellent.
    One other issue for the OP: the act of flipping on an FPE breaker can pull them away from the busbar. This is especially problematic with the FPE thin breakers, where only two small fingers are pushed into a busbar hole. If the panel cover isn't tight against the breaker, you can pull it lose just by turning it on. For most other breakers, turning on the breaker pushes the contacts onto the busbar. Often these panels (in California) are on the same garage wall as the garage entrance from the home. I've seen numerous instances of circuits going on and off from the door being shut.
    My advice: Replace the panel or refuse to work on it.
    ABC
    "Eschew Obfuscation!"
  5. #15
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by drcampbell View Post
    Possible reasons:
    - Too much current
    Seen 22kAIC breakers (single pole 20A) hold under fault until the wire exploded... shouldnt the instantaneous trip rating of a breaker be lower than the point in which the circuit wiring becomes a fuse? I thought the AIC rating was to keep the breaker from exploding under fault.
  6. #16
    Join Date
    Dec 2008
    Oklahoma
    Posts
    664
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I have found...
    That the size of the Kaboom Decreases the futher away from the panel ......... a long lenght of wire will Choke the amount of current (Kaboom capability)
    I most current that I have seen on a 12 ga wire was approx 90amps( inrush of two motors starrting at the same time), It held for approx 2 mins before tripping a cold G.E. 20 amp snap-in.
    When ever I see 60+ amps on a 20 amp breaker, I will go look for a locked up motor/rotor, or, it is a Dead short wire that has "welded" itself to ground
    I was working with another sparky whom shorted out a wire while we working, and without looking I bet him lunch that it was a square D QO panel judging just from the "Little amount of Spark" ( more of a 'click' than a' kapow") from the fault.... Boy that cheesburger tasted good.
  7. #17
    Join Date
    May 2011
    Posts
    4,960
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I'm curious what evidence people can point to regarding the UBI breakers. Good, better, or not better all?
  8. #18
    Join Date
    Jul 2006
    Posts
    8,387
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    The Interrupting Current (IC) rating has nothing whatsoever to do with trip time, it's strictly the point at which, mechanically, the breaker comes to pieces from the magnetic forces involved.
    Typical instantaneous trip setting is 10X the breaker rating, but there is no universal rule, I've seen some resi breakers that are as low as 4X. So on a 20A breaker that is between 80A and 200A current before it trips. Even then, there is a fairly wide tolerance band for the trip times plus there is the actual clearing time, the time it takes for the contacts to open far enough to stop the current from flowing. But to your point, yes, the trip curve is SUPPOSED to be lower than the damage curve of the conductors it's meant to protect, but that's thermally. Once you are acting in the instantaneous range, all bets are off. So yes, I too have had some large conductors vaporize on me AS the breaker was tripping on instantaneous. It's not fun...
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  9. #19
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,226
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It is.
    For the commonly used 10k and 22k devices the AIC rating has nothing to do with the 'tripping' of the device.
    I don't think there has been any significant advances in miniature molded case breakers in more than 50 years. I doubt they are as inherently unsafe as many anecdotal tales make them out to be.
    Just because you can, doesn't mean you should.
  10. #20
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,030
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    The only thing it has to do with tripping is that it must be able to trip under that current without blowing up or failing closed. It must be able to safely interrupt (the I in AIC) that current.