ok, we installed a 2' x 3' j-box,we have 3 - 3" EMT'S on 1 side of box and 3 - 3" EMT'S on the opposite side of box " but" they are not directly across from one another they are "offset" a bit ,instead of a straight across from each other,in other words the wires will have a offset going into other conduits....dont you still classify that as a "straight pull" not a "angle " pull ???? *
so it should be 6x3=18+3+3 = 24" minimum size of box ...correct?