    Hello guys,
    I am really confused about the answers of some questions given by my instructor. These answers are from the instructor's version of NEC Prep book.
    Here is one pair of some questions/answers:
    Question:
    A 3-phase 36KVA load rated 208V is wired to a panel board with 80ft lengths of 1 AWG THHN aluminum. What is the apprx Voltage drop of the feeder circuit conductors?
    Answer (from the book):
    I = 36000VA / 208V = 173AEvd = (1.732*K*I*D)/cmil = (1.732*21.2*173*80)/83'690 = 6.07V
    My answer:
    Ok because this is a 3-phase system, so P-in = (Sqrt of 3 * E-line * I-line) = (3 * E-phase * I-phase)
    I-line = P/(1.732*E-line) = 36000/(1.732*208) = 100A
    Evd = (1.732*21.2*100*80)/83'690 = 3.51V
    The confusion is: why did the author use single phase power formula in a 3-phase system calculation? If the author is right and I'm wrong, please explain. I'm not very convinced that my instructor said I was wrong in my calculations just because the book had different answers.
  2. #2
    Join Date
    Jul 2005
    Tennessee
    Posts
    15,540
    In their calculation it appears they are using single phase amperage for the 36kw.
    I get the same number you do.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  3. #3
    Join Date
    Feb 2017
    Texarkana, TX, USA
    Posts
    3
    Quote Originally Posted by augie47 View Post
    Thank you for your reply, but I really need some one who can help me to clear this mess up, because I no matter what I tried to explain, my instructor would stick to the answers in his book.
    10 out of 10 questions, the author used P = I * E for all the 3-phase calculations. Just what the heck?
    I don't want to make my instructor mad, but I want it to be right, and ultimately I don't want to get a big Zero on my paper just because some else made mistakes in his damm answer keys. This is really frustrating.
  4. #4
    Join Date
    Apr 2007
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,364
    Quote Originally Posted by mhuytran View Post
    this is a key part of your training. dealing with AHJ over a disagreement.
    consider it useful to learn how to move past a situation blocked by
    someone who won't change either the subject, or their mind.
    it's just hidden in the middle of classwork.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~
  5. #5
    Join Date
    Jan 2016
    PA
    Posts
    4,805
    ask him to do the calculation using I calculated from kva and the Ohm/1k ft value from the NEC tables
    he must acknowledge S kva = sqrt3 x V x I ???
  6. #6
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    18,765
    Quote Originally Posted by Ingenieur View Post
    Where V = line-to-line voltage and I = line current, not "phase current" which is slightly ambiguous because some call A a phase and while others call AB a phase and some are just inconsistent in their language.
  7. #7
    Join Date
    Jul 2005
    Tennessee
    Posts
    15,540
    as mentioned, IMO, he is using the wrong number for "I", the 3 phase current.
  8. #8
    Join Date
    Feb 2017
    Texarkana, TX, USA
    Posts
    3
    I asked my instructor where the answer keys were from. He said they were from "the author" (hrmm... i.e Mr. Mike Holt)
    Course code is <ELPT-1429>, Chapter 4, HandOut 1 with 5 originals + 5 extras.
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts