Do I Need Conduit?

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
If you new that you had to run 8/4 (3 current carrying plus one ground wire) AC, MC, or flex cable to a piece of equipment, white size cutout would you want to see?

No cutout is not an option. I know what the wire size is, I know the type of conduit they will likely run, but I do not know the fittings you will use to connect to the chamber. I am wanting to provide you with a cutout, but I am not sure what size to make the cutout...

What is it feeding? If a motor then your switch might need a horsepower rating, otherwise at least a rating greater or equal to the load.
 